Trane heat pump tripped breaker twice

Reply

  #1  
Old 05-29-16, 10:36 PM
J
Member
Thread Starter
Join Date: May 2016
Location: USA
Posts: 3
Received 0 Votes on 0 Posts
Post Trane heat pump tripped breaker twice

Trane 4TWX3036A

Unit is 12 - 15 year old. It was raining. Opened the cover, found a dead mouse on the capacitor. The service brochure was chewed to pieces. Cleaned everything, blow-dried everything, and rest the breaker. Run for 10 seconds. Heard a pop and saw a flash near the base. Wonder if the compressor is grounded, or some wire damage. Ordered a capacitor, which should arrive in a few days.

Can anyone post a wire diagram? Thanks.

Any guidance and speculations on potential problems are appreciated.
 

Last edited by PJmax; 05-30-16 at 02:36 AM. Reason: added model to text
  #2  
Old 05-30-16, 02:41 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 61,440
Received 1,412 Votes on 1,306 Posts
Welcome to the forums.

I moved your thread here to the heat pump forum. I'm searching for the diagram now.
 
  #3  
Old 05-30-16, 03:26 PM
J
Member
Thread Starter
Join Date: May 2016
Location: USA
Posts: 3
Received 0 Votes on 0 Posts
Trane heat pump tripped breaker twice - Follow up

Trane heat pump tripped breaker twice - Follow up
Measured Compressor Ohms:
Red wire to ground, infinite;
Black/light blue to ground, 1.7k approx;
Light orange to ground, zero

Can I assume compressor is OK?

I figured the spark/flash is from outside the unit near the base, where the 240 volt feed is. I assume the cable insulation is burnt and grounds in rain. I am replacing the cable and see if it'll fix the problem.

More to follow.

BTW, the capacitor may be still OK but in pretty bad because the little chipmunk (perhaps not a little mouse as I originally thought) rested in peace on it.
 
  #4  
Old 05-30-16, 03:40 PM
Geochurchi's Avatar
Temporarily Suspended
Join Date: Nov 2012
Location: United States
Posts: 5,006
Received 89 Votes on 84 Posts
Before you replace the cable remove it from the contractor insulate the ends and reset the breaker,if the breaker resets then the cabling is fine.
 
  #5  
Old 05-30-16, 03:57 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 61,440
Received 1,412 Votes on 1,306 Posts
Black/light blue to ground, 1.7k approx
There should be no continuity from any terminal to ground. Some leakage may be normal but I'm not sure what the value is for Trane compressors. We'll find out.

I'm a little surprised you're seeing continuity to ground on only one terminal. The motor windings are so low you should measure 1.7k on all terminals.

You should also check continuity between the windings like shown below. You may not get the same exact readings but the two windings added together should be equal to the highest value you measure. There should be no wires on the compressor when checking.

Safety glasses should be worn when working on the compressor connections in case of refrigerant rupture.

Name:  comp.jpg
Views: 150
Size:  14.8 KB
 
  #6  
Old 05-30-16, 09:36 PM
J
Member
Thread Starter
Join Date: May 2016
Location: USA
Posts: 3
Received 0 Votes on 0 Posts
Post Thank you, Pete. I'll check the compressor again.

The cable seems to be shorted when wet - I could be wrong. I saw a spark coming from the area.

Where do I go for SEU THHN (THWN) #6 CU 3-conductor cable?
 