Need help installing thermostat - Honeywell RTH3100C


  #1  
Old 12-06-16, 07:37 PM
K
Member
Thread Starter
Join Date: Oct 2000
Location: Livonia, Michigan
Posts: 894
Upvotes: 0
Received 0 Upvotes on 0 Posts
Need help installing thermostat - Honeywell RTH3100C

Can someone give me the proper connections for my thermostat? The a/c / heat pump is a Rudd model (-AKA, -ALB, -AMB).

There are four wires coming from the wall (red, white, green, yellow).

They were connected to the old White Rodgers model 1F80-361 as follows:

G - green
Y - yellow
W - white
RC - red
RC to RH jumpered

The new Honeywell RTH3100C has the following connections available:

E, Aux, Y, G, O, L, R, B, C
 
  #2  
Old 12-07-16, 08:08 AM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
With only four wires at the stat it's not a heat pump.
 
  #3  
Old 12-07-16, 09:52 AM
K
Member
Thread Starter
Join Date: Oct 2000
Location: Livonia, Michigan
Posts: 894
Upvotes: 0
Received 0 Upvotes on 0 Posts
There is a fifth blue wire coming from the wall, but it wasn't hooked up to the old thermostat.
 
  #4  
Old 12-07-16, 10:15 AM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
The blue wire is spare wire which you might need for a new stat. The stat you bought is for a heat pump. I would take it back and get an RTH 6000 or higher.
 
  #5  
Old 12-07-16, 11:17 AM
R
Member
Join Date: Oct 2016
Posts: 2,144
Received 187 Upvotes on 171 Posts
  #6  
Old 12-07-16, 12:01 PM
K
Member
Thread Starter
Join Date: Oct 2000
Location: Livonia, Michigan
Posts: 894
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes it is. I already have it hooked up and running the a/c. I tried to run the heat, but it's either not heating, or it's too warm to verify function. It was 78 deg in the unit here in Florida. I set it to 81, but it never got warmer.

Right now, this is the way I have it hooked up:

Y - yellow wire
G - green wire
R - red wire
Aux - white wire
E and Aux jumpered
blue wire left unconnected

I ran it with and without the E to Aux jumpered. It seemed to make no difference.

I'll admit I don't know if the unit has a heat pump. I don't know how heat is provided.
 
  #7  
Old 12-08-16, 05:08 AM
S
Member
Join Date: Feb 2014
Location: USA
Posts: 1,771
Received 0 Upvotes on 0 Posts
You need to connect the blue wire to C terminal on the stat. We will need the model number on the furnace to tell you where to connect the blue wire at the furnace.
 
  #8  
Old 12-09-16, 07:59 AM
K
Member
Thread Starter
Join Date: Oct 2000
Location: Livonia, Michigan
Posts: 894
Upvotes: 0
Received 0 Upvotes on 0 Posts
I don't believe anyone has a conventional furnace in South Florida. Certainly no gas or oil hooked up to our condominium complex.
 

Last edited by Kestas; 12-09-16 at 09:16 AM.
  #9  
Old 12-09-16, 12:26 PM
K
Member
Thread Starter
Join Date: Oct 2000
Location: Livonia, Michigan
Posts: 894
Upvotes: 0
Received 0 Upvotes on 0 Posts
Fixed! I got the proper thermostat - a Pro1 T701 model. Hooking it up was straightforward. I now have heat as well as a/c. Thanks for the help.
 
 