Neutral wire for line voltage stat

I am changing an old Honeywell t4309 to a hotel tech lt120a but cannot figure out the neutral wire. Both have 6 whites and are wired as follows:
Honeywell (was installed)
Red-load cool
Brown-load heat
Blue-fan lo
Tan-fan med
Yellow-fan hi
Orange-hot line

Hotel tech (swapping in)
Black-line
White-neutral
Red-heat
Blue-cool
Yellow-low fan
Orange-high fan

I cannot figure out the neutral wire
 
  #2  
Old 12-09-16, 08:05 AM
C
Member
Join Date: May 2015
Location: USA
Posts: 3,107
Received 145 Upvotes on 118 Posts
The Hotel tech unit requires a neutral connection and the Honeywell didn't. This is probably to power the display and internal circuitry.

If there's no neutral wire in the box you will either have to rewire or look for a line voltage thermostat that doesn't require a neutral.
 
  #3  
Old 12-09-16, 08:54 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,950
Received 3,760 Upvotes on 3,371 Posts
You may be able to convert the spare wire to neutral but you'd need a wiring diagram for the FCU.
 
  #4  
Old 12-09-16, 11:54 AM
B
Member
Thread Starter
Join Date: Mar 2015
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
Wink Diagram

Ft Name:  image.jpg
Views: 263
Size:  37.3 KB
I think I found the diagram on the unit if that helps
 
  #5  
Old 12-09-16, 12:10 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,950
Received 3,760 Upvotes on 3,371 Posts
That helps tremendously but it's unreadable. Take two pictures...... closeup.
One of the controls section like below and one of the thermostat.

The N is neutral and I've traced it in white. There is a setscrew for white on the terminal strip. The red circle is the connecting terminal strip. You could probably move the tan to neutral.

if you do.... you MUST make and leave a notation near the control board for future service.

Name:  image.jpg
Views: 589
Size:  43.5 KB
 
  #6  
Old 12-09-16, 01:38 PM
B
Member
Thread Starter
Join Date: Mar 2015
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
Photos

Name:  20161209_143003.jpg
Views: 187
Size:  37.7 KB
Hope these are clearer
 
  #7  
Old 12-09-16, 01:41 PM
B
Member
Thread Starter
Join Date: Mar 2015
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
Other pic

Name:  20161209_143009.jpg
Views: 185
Size:  41.4 KB
Let me know if you need any other pictures
 
  #8  
Old 12-09-16, 01:47 PM
B
Member
Thread Starter
Join Date: Mar 2015
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
More pics

Here's the wiriName:  1481316369885-695586090.jpg
Views: 207
Size:  25.2 KBng let me know if you need anymorr
 
  #9  
Old 12-09-16, 02:41 PM
B
Member
Thread Starter
Join Date: Mar 2015
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
Worked

Thanks for the help I really appreciate it! I really wanted to put in a nest but it cannot handle 120v
 
  #10  
Old 12-09-16, 03:46 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,950
Received 3,760 Upvotes on 3,371 Posts
You could put a nest in but every function needs to be controlled with a 120v/24v relay.
 
  #11  
Old 12-09-16, 05:10 PM
B
Member
Thread Starter
Join Date: Mar 2015
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
Pete would I just put a relay on all 6 wires? In order to wire in a nest?
 
  #12  
Old 12-09-16, 05:19 PM
B
Member
Thread Starter
Join Date: Mar 2015
Posts: 11
Upvotes: 0
Received 0 Upvotes on 0 Posts
Name:  image.jpg
Views: 198
Size:  19.6 KB
What relay would you suggest and what wires would go where?
 
 