Frequent aux heat usage
#1
Member
Thread Starter
Join Date: Nov 2015
Posts: 14
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Frequent aux heat usage
Hello I'm not sure if my thermostat is functioning correctly or not it seems to be relying a lot on the auxiliary heat. The temperature had been dropping down in the teens here lately and I though that could be the issue but every time my heat will run for about a minute or two then the thermostat will kick the aux on and continue to run for several minutes before shutting off at the programmed 65F. My unit is a Bryant 2 ton with heat pump and the thermostat is a Honeywell rthl2500 thermostat and there are 2 wires that aren't connected to it(brown & black)could that have anything to do with it? I installed the thermostat this summer. I posted some pics of the thermostat and manual to see if anyone could find anything wrong.
https://i.imgsafe.org/c03c80ff9b.jpg
https://i.imgsafe.org/c03c1861f2.jpg
https://i.imgsafe.org/c03c80ff9b.jpg
https://i.imgsafe.org/c03c1861f2.jpg
#3
Member
Thread Starter
Join Date: Nov 2015
Posts: 14
Upvotes: 0
Received 0 Upvotes
on
0 Posts
No it stays set at 65 at all times at the moment does anyone have experience with Bryant wiring colors from what I've found it looks like I have 3 common wires( brown black and blue) which can't be correct.
#5
Member
Thread Starter
Join Date: Nov 2015
Posts: 14
Upvotes: 0
Received 0 Upvotes
on
0 Posts
I'm at work at the moment, but I can if they consider the blue wire as just B it looks like shouldn't be used with this thermostat since I have the orange wire according to the manual I will try it when I get home
#6
The wiring colors don't necessarily mean a thing. The color could be assigned any function.
You need to go to the air handler..... locate where the thermostat wires enter the unit..... remove the service door and visually see where they are connected.
What model stat is that...... rthl2500 ???
Your wiring could be neatened up and the white and blue wires in W/Aux does not look correct.

The stat also needs to be programmed for heat pump with aux heat.
You need to go to the air handler..... locate where the thermostat wires enter the unit..... remove the service door and visually see where they are connected.
What model stat is that...... rthl2500 ???
Your wiring could be neatened up and the white and blue wires in W/Aux does not look correct.

The stat also needs to be programmed for heat pump with aux heat.
#7
Member
Thread Starter
Join Date: Nov 2015
Posts: 14
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Just got home and opened it up and there is no B wire connected on the board, and where it comes into the unit it looks like the blue wire is spliced into the white wire, its. 664anx unit
https://i.imgsafe.org/c7068480a2.jpg
https://i.imgsafe.org/c70640ab98.jpg
https://i.imgsafe.org/c7068480a2.jpg
https://i.imgsafe.org/c70640ab98.jpg
#9
So you can tape off the blue at the stat.
The heat pump should run and stay running even if the heat strips come on. The heat strips will come on when the actual room temperature is three or more degrees below the setpoint.
What you could try is to just run the heat pump...... temporarily disconnect the white wire and see what happens.
The heat pump should run and stay running even if the heat strips come on. The heat strips will come on when the actual room temperature is three or more degrees below the setpoint.
What you could try is to just run the heat pump...... temporarily disconnect the white wire and see what happens.
#10
Member
Thread Starter
Join Date: Nov 2015
Posts: 14
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Ok I taped off the blue wire and left the white in the aux port tried increasing the temp by 1 degree and heat came on and ran without the auxiliary coming on, tried increasing it 5 degrees and the auxiliary heat came on like its supposed to, guess I'll ok find out tonight if it's working right
#11
http://dms.hvacpartners.com/docs/100...664A.24.1B.pdf
Looks like you have a 20 year old package unit.
There is a decent diagram in the heat pump manual.
The newer Honeywell Redlink VisionPro TH8320R and TH8321R allow you to adjust the demand required before the heat strips become energized. The savings from this function can pay for the thermostat in one season.
This function is not available on the RTH2510 or RTH2410.
http://pdf.lowes.com/installationgui...85_install.pdf
Looks like you have a 20 year old package unit.
There is a decent diagram in the heat pump manual.
The newer Honeywell Redlink VisionPro TH8320R and TH8321R allow you to adjust the demand required before the heat strips become energized. The savings from this function can pay for the thermostat in one season.
This function is not available on the RTH2510 or RTH2410.
http://pdf.lowes.com/installationgui...85_install.pdf
#12
Member
Thread Starter
Join Date: Nov 2015
Posts: 14
Upvotes: 0
Received 0 Upvotes
on
0 Posts
https://i.imgsafe.org/caf60ded97.jpg
I found the old thermostat in the garage and the blue line must have been labeled as an E connection so I did have it wired right according to page 24 of the manual included with the thermostat in the 1st set of pictures so I don't known where the problem is
I found the old thermostat in the garage and the blue line must have been labeled as an E connection so I did have it wired right according to page 24 of the manual included with the thermostat in the 1st set of pictures so I don't known where the problem is
Last edited by Stefan256; 12-10-16 at 06:45 PM.
#13
The heat strips will be energized any time the heating demand is 2 degrees.
Using a programmable thermostat to change the heating setpoint throughout the day will energize the heat strips and cost more to operate.
Using a programmable thermostat to change the heating setpoint throughout the day will energize the heat strips and cost more to operate.