thermostat issue with heat pump


  #1  
Old 10-15-17, 02:05 PM
X
Member
Thread Starter
Join Date: Dec 2011
Location: Usa
Posts: 231
Upvotes: 0
Received 0 Upvotes on 0 Posts
thermostat issue with heat pump

I have a goodman heatpump, this summer I changed my thermostat over to a new honeywell thermostat. All summer long the cooling side work without issue. Today I went to try the heat side, when calling for heat the blower will activate, but the compressor will not kick on. I did not have this issue with the older thermostat. The thermostat is wired up correctly, and the only way I can get the system to function properly is if I add a jumper between blower and compressor. This way, when in heat mode and the blower kicks on, it sends signal over to the compressor and starts it. The reversing valve works fine between cool/heat, it just seems that the thermostat is not sending power to the compressor when calling for heat.

The thermostat does have a switch on the back for gas/oil or heat pump and I have tried both settings with no change.

heat and cool both work fine with the jumper wire in place.
 
  #2  
Old 10-15-17, 02:20 PM
Houston204's Avatar
Forum Topic Moderator
Join Date: Oct 2009
Location: Texas
Posts: 6,479
Received 90 Upvotes on 83 Posts
What is the model number of your new thermostat?
 
  #3  
Old 10-15-17, 03:49 PM
X
Member
Thread Starter
Join Date: Dec 2011
Location: Usa
Posts: 231
Upvotes: 0
Received 0 Upvotes on 0 Posts
Not sure on the model, it doesn't say anywhere on it. It is just a basic programmable thermostat that i bought at home depot.
 
  #4  
Old 10-15-17, 03:58 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,820
Received 3,745 Upvotes on 3,359 Posts
It's on the back of the stat.
 
  #5  
Old 10-15-17, 04:02 PM
X
Member
Thread Starter
Join Date: Dec 2011
Location: Usa
Posts: 231
Upvotes: 0
Received 0 Upvotes on 0 Posts
Okay, I found it, its the RTH2410B. I actually just figured it out, I needed a jumper between Y and W, now it works.
 
  #6  
Old 10-15-17, 04:14 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,820
Received 3,745 Upvotes on 3,359 Posts
If you have an orange wire on O/B.... then the jumper on the back gets set to O. The fan jumper needs to be in the HE location.

Go to system setup and change function 6 to 1.
 
 