Heat pump clicks but wonít turn on

Iím sure itís been tackled before but I cannot find the answer for my specific problem. We have a heat pump that was working fine up until the beginning of this cold season. The unit is a 2 1/2 year old air ease heat pump. When it goes into heating mode it clicks outside, the air handler fan turns on but is just recirculating air until the temp drops enough that the auxiliary heating kicks in. I know the fan works outside because if you press the contactor everything turns on as it should and it will begin heating. If I jump the orange (o/b) and red wire it still just clicks as well as orange, yellow, white, and red. Currently I have the heat pump unhooked at the thermostat and am just using the aux heating. Iím not sure what I need to test next to try to get this thing working again, any help would be really appreciated!
 
Sponsored Links
  #2  
Old 11-30-18, 06:07 PM
Member
Join Date: Oct 2016
Posts: 1,329
Received 33 Votes on 30 Posts
Let’s start from the beginning.
Using your meter, check for a heating call at the outdoor unit.
Don’t manually close the contactor. It’s dangerous and could potentially harm the unit.
 
  #3  
Old 11-30-18, 10:13 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 52,721
Received 345 Votes on 323 Posts
Welcome to the forums.

It sounds to me like you are low on refrigerant. There are high and low pressure switches that monitor system pressure. If it's low...... it won't start automatically.

If you want to confirm this. You'll need to locate where the thermostat wiring connects from the house to the outside condenser. It may be in the electrical connection area. The wires should be connected with wirenuts. Set the stat to cooling or connect the yellow(Y) wire to red(R) wire. Test the red and yellow wires at the wirenut splice for 24vAC. If it's there..... the problem is inside the condenser and probably low refrigerant. If you don't have the 24vAC.... you'll need to trace it back inside the house.
 
  #4  
Old 12-01-18, 06:15 AM
Member
Thread Starter
Join Date: Nov 2018
Location: Usa
Posts: 2
Received 0 Votes on 0 Posts
Alright, I went out and tested everything. Iíve got 24 volts. Iím leaning towards the refrigerant being low as we had to have a repair made this summer for leaking referigerant twice. I hadnít even considered that, I just assumed it was fixed since it worked the rest of summer with no issues. Looks like Iíll be calling them back to look it over again. Thanks a lot!
 
Reply

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
Display Modes
 
Ask a Question
Question Title:
Description:
Your question will be posted in: