Tempstar air handler

I have a model FEM4P3600AT. With the system off and the blower/ fan set on auto, the fan quit shutting off.
It appears to be the fan motor. I have been told it is a smart motor that has a circuit board on it and something is wrong with that. The motor runs beautiful.
Can I keep the motor and add a relay for the fan control 24v?
 
  #2  
Old 11-09-20, 05:56 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,139
Received 3,619 Upvotes on 3,245 Posts
You need to check the 24v speed taps to see if one is staying active.
That would keep the motor running.

Tempstar FEM4P tech manual (pdf)
 
  #3  
Old 11-09-20, 07:38 PM
P
Member
Thread Starter
Join Date: Apr 2019
Location: United States
Posts: 11
Received 0 Upvotes on 0 Posts
That's what it is. I was told it is in the board on the motor and I need a new motor. I was quoted a new "smart" motor for $755.00 or a new board for $580.00 or a generic motor, without the board and a relay for $542.00. I was wondering if they can put a generic motor, and a relay, why they couldn't use the old good motor and a relay.
 
 