Hello, so my heater started blowing cold air, I called out an HVAC company and the tech told me the contactor was bad and showed me. It glowed and was burnt out. I opted to change the part myself due to the price. Here is where I am now.
DPC single pole switched out for a double pole. For a few hours the heat came out then back to cold air. I inspected the contactor and it seemed fine.
Next day, I checked the large capacitor next to it and it was bad. I verified it with a ESR meter. I replaced it and now the unit fan turns on then off, off/on...
I have the schematic and was following the troubleshooting guide but this new problem is not listed. I will be going into the attic to look over the equipment up there and continue following the troubleshooting guide.
My question is has anyone have a problem like this and what might I look at next? Thanks
Goodman
ARUF486016- air handler
GSZ130601ab- heat pump
Hi, what contactor was glowing red? What is a DPC switch? this is a strange description of the operation.
This is a HP and when the thermostat is calling for heat what happens next?
Geo 🇺🇸
Geochurchi
Thanks. DPC is Definite Purpose Contactor. The red marks are where it glowed but not all the areas in red. Just the top and bottom but I dont recall which ones. When I set the thermostat to heat, it blew cold air only when I replaced the DPC for a 2 pole. It did that for 4 hours straight. I turned it all off and went to bed. When I checked it this afternoon, I found the capacitor next to it was bad. I changed it out and now it is doing the on off thing. Short cycling I guess.
PJmax
Thank you.
I was thinking that but I did read something where a 2 pole was fine. It was suggested by the store when I bought it. I was thinking of changing it out but why did it seem to operate when I replaced the DPC?
I am in Arizona, the coldest it has been is around freezing. I had cold air coming out but then it started to warm up and I went to dinner. When I cam back it was blowing cold air.
This is the wiring diagram I think you want.
I didnt make it up to the attic, I want to look at the filter up there and the whole unit. I have to take this up tomorrow after work. I appreciate the help. Thanks.
If your unit has a crankcase heater..... it does require a single switched contactor. I can't tell from the diagram if you have one. It's optional in areas that aren't considered cold zones.
Is just the condenser fan cycling...... the compressor is not cycling ?
The condenser fan is controlled from the defrost board.
As I mentioned.... it sounds like you have a defrost problem.
I used blue for black for clarity. This is the crankcase heater circuit.
It shows a contactor with L1 shorted to T1.
Have a 2-year old mini-split system which is having some problems. Having a technician come out to address, but I like to make sure I'm informed enough to talk to them.
The system works fine for a while (heat), but after a while starts blowing cold air. Shutting off all the units, then restarting each One of the indoor units seems to be icing up, as there was an icicle hanging from it. The outdoor unit looks normal, it's not covered by snow/ice or anything unexpected.
I know with AC, freezing coils often indicates low refrigerant. But I've never considered a heat pump freezing up in the winter.
FYI, it's not all that cold here. 32 degrees, and the units are Mitsubishi "Hyper Heat", so outdoor temp shouldn't be an issue.
Last summer I got a heat pump system (Daikin, inverter, if this helps). The system cools perfectly, but I’m having trouble with the heat.
I usually set the heat to 65F, but once the system reaches that temperature it continues to heat. I’ve had the set temperature as low as 62, but the room temperature has gotten as warm as 72. At night, I’ll have to turn the system off because the house will be too warm.
I’ve briefly messed around with the auto setting and it seems to work just fine. I set it to Heat at 65, Cool at 70 and it keeps the house at a nice 67/68.
I called the installers out, they checked the system and replaced the thermostat. But I’m still having this problem. Is it user error? Or is this a problem with the system?
I look forward to hearing from all of you.