The circuitry looks to be 240v.
That would mean you have one 2P breaker that controls the heat.
Probably a 2P20A breaker.
Did you want to change the thermostat too ?
Are all three baseboard heaters on this controller ?
Please supply the linear footage of the three so we can calculate combined current.
The Aube controller is good for 22A at 240v........ Aube RC840T-240
So you're actually just over the limit of the circuit.
4500w = 18.75amps
Code now requires electric baseboard heat to be figured at continuous load which means a max of 16 amps on a 20 amp circuit.
20 Amp dbl break with 2 wires coming off either side
Does that mean 4 wires on a two pole breaker ?
I see one switching relay.... where would the second set of wires go ?
The Aube unit would replace what you have at that location and give you a C connection for a programmable thermostat.... not a wifi thermostat. I only see two wires to the thermostat so you could use a battery programmable.
Does that mean 4 wires on a two pole breaker ? I see one switching relay.... where would the second set of wires go ?
Sorry, only 2 wires total coming from the breaker; it’s a old pushmatic, which somewhere down the line I want to address with an electrician.
i could try running 2 units to deal with the code requirement. We just want to get the draft out of the room when it’s colder out. Another possibility would be to have a 30 amp breaker installed when we get the service updated. We have lived here for 30 years and all the homes being sold now are being torn down and replaced with 2 story homes. We plan on moving in the next 5 years.
this gives me enough to update the relay, and safely have heat in the room for now.
If your system has been running ok.... don't fix what ain't broke.
Pray the Pushmatic doesn't crap out.
You can use the Aube. You can gut your relay box and put it inside or replace that box with a 4" deep square box. I can draw you a diagram for which ever you want to do.
We have a new Trane heat pump installed last February, so less than a year old. This year we have noticed a strong odor coming from the vents when the heat is running and the outside temperature drops below 34 degrees (give or take a couple degrees). The blower unit is in the crawlspace which stays dry with a steady low humidity. Last winter when the unit was installed there was no odor during the heat cycle. The Trane installers did come out and thoroughly inspected everything including the coils and drain pan etc. and put it through several cycles including the defrost cycle, but could not replicate the issue, although it was in the middle of the day and the outside temperature was above 45 degrees when they came out. Now every time the temperature drops in the 30’s, the smell is back. They said they’ll had to come back when it’s colder during the day to try to smell the odor since they couldn’t replicate it. Any insight? We can’t be the only ones with this issue. Read More
Hi all! I need some hvac help. My husband and I are building a house (not our first rodeo) and we're nearly finished but now we have a small-ish issue.
We have a Goodman Air handler and a few weeks ago my husband was an idiot, and accidentally cut the wire that supplied the power to the unit.
I managed to fix that issue and got it up and running again.
A day or so later there was no power to the thermostat (Nest). I replaced the batteries and tested power to the air handler and heat pump, both were fine. It ended up being one of the 3 amp fuses that had blown. I replaced it and was super happy that I had solved the problem.
Well, the next night I saw on the Nest app that there was no power to the thermostat again. Sure enough, the E0F Error is back.
I changed the fuse again after realizing that some of the low voltage wires had been touching and one was a bit loose (like in the pic shown) and we had no issues for about a week, then the fuse blew again and the cool cloud app showed that either the condensate tray was full (it was dry) or the auxiliary input was open.
[img]https://cimg3.ibsrv.net/gimg/www.doityourselft.com-vbulletin/2000x1504/img_9514_68b2f6b1e14d218187dfdf1b47c91ca36718ce78.jpeg[/img]
[i]This was taken before I fixed the wires from touching/tightened them up[/i]
[img]https://cimg4.ibsrv.net/gimg/www.doityourselft.com-vbulletin/920x2000/img_9641_30d15ce57231ee23d52d9a41eac75f656320448a.png[/img]
[i]Error codes from the cool cloud app[/i]
This is new construction and we need to get our final very soon, so I need to solve the problem ASAP.
Thanks!
[img]https://cimg9.ibsrv.net/gimg/www.doityourselft.com-vbulletin/596x288/img_9514_pj_932cb6232524eb0e812acaa67552c2cf042a9893.jpeg[/img]Read More