I am going to run a 220v circuit to the garage. It will have two woodworking machines running at a time, a dust collector and whatever tool I am using. The run will be about 80'counting the actual path of the wire. What size wire do I need and what size breaker?
 
  #2  
Old 01-22-01, 05:32 AM
Guest
Visiting Guest
Posts: n/a
Your breaker size will depend on your wire size--which will depend on what you are running--what are the amps rating of these tools?
 
  #3  
Old 01-26-01, 12:55 PM
Gary Tait
Visiting Guest
Posts: n/a
50A breaker, #6 wire, subpanel in shop with 20A breaker
for extractor, 20A breaker for tools, both wired with #12
wire.
 
  #4  
Old 01-29-01, 11:21 AM
plumldk1
Visiting Guest
Posts: n/a
Thanks Gary. I'll use your recomendation. I have #10 wire, so I'll use it instead of the #12.
 
  #5  
Old 02-08-01, 10:58 AM
abNORMal's Avatar
Member
Join Date: Nov 2000
Location: New Jersey USA
Posts: 535
Received 0 Votes on 0 Posts
Lightbulb

plum:
Be sure to wire this panel as a subpanel, not a main, which means that you will want to separate the neutral bus from the grounding bar, and run a ground from sub to main. (If the garage is detached and there is no other common ground between the two buildings, you have alternative grounding methods). Check the Electrical forum for discussions on wiring outbuildings and grounding subpanels.
 
 