I would like to install a humidifier in my home
I was looking at the AprilAire model 600
my home is only 1350 Sq Ft so i think it would be adequete.
My question is what else do i need to do the installation?
Can this Unit be mounted in eiter direction??
I see that there is a A50 relay that may be needed and one site even sells an installation kit that include the copper tubing and wiring etc.
I have a Armstrong Ultra SX80 furnace
Any other tips on installation would be appreciated
thanks
I was looking at the AprilAire model 600
my home is only 1350 Sq Ft so i think it would be adequete.
My question is what else do i need to do the installation?
Can this Unit be mounted in eiter direction??
I see that there is a A50 relay that may be needed and one site even sells an installation kit that include the copper tubing and wiring etc.
I have a Armstrong Ultra SX80 furnace
Any other tips on installation would be appreciated
thanks
#2

For sure get the A50 relay .Then you dont have to go into the blower wiring. It just slips over the blower wire. i like to tapinto a hot water link if I can. For the 1/4" line and tap in Id go to Home depot or Lowes for it. Then you can get it how long you need.
ED
ED

#3
i mount the 600 on the supply and duct it over to the return. this allows more moisture pickup due the "blow" rather that "suck" through the media, to put it plainly
model 50 relay will sense ampdraw through the heat speed fan wire and close so 600's valve does not open with call for heat but no fan (fan startup delay is up to 90 seconds) it must be used
BUT
if the board on your unit has a HUM terminal, this will typically energize the terminal with 120 volts when heat AND fan are on. using the transformer in the 600 box, you can power it here (and common) thereby only sending 24 volts to the humidistat when these conditions are met, bypassing the need for the model 50.
hope this did not confuse you
model 50 relay will sense ampdraw through the heat speed fan wire and close so 600's valve does not open with call for heat but no fan (fan startup delay is up to 90 seconds) it must be used
BUT
if the board on your unit has a HUM terminal, this will typically energize the terminal with 120 volts when heat AND fan are on. using the transformer in the 600 box, you can power it here (and common) thereby only sending 24 volts to the humidistat when these conditions are met, bypassing the need for the model 50.
hope this did not confuse you

#4
Well i ordered the 600 and the a50 relay (only 27 bucks fro the relay),
unfortunately i dont think i have enough room to mount the unit right on the supply duct
Is there a noticeable difference mounted on the supply as opposed to the return??
If it were mounted on the supply why would one duct it over to the return, would you want the humid air flowing through the supply with the dry air??
unfortunately i dont think i have enough room to mount the unit right on the supply duct
Is there a noticeable difference mounted on the supply as opposed to the return??
If it were mounted on the supply why would one duct it over to the return, would you want the humid air flowing through the supply with the dry air??