Honeywell 220 - Is sail switch needed with Trane furnance?
How can I tell if the Sail switch is needed for the humidifier install? Directions state some furnaces don't need sail switch. Furnace: TraneXR90 (UX-C)
Thanks!
Also, is it better to hook to hot or cold water line? How many gallons flow through in a cold day with the furnace running?
Thanks!
Also, is it better to hook to hot or cold water line? How many gallons flow through in a cold day with the furnace running?
#2
Photo below is mine.. behind this cover (Turn power OFF), there a wire taped "HUM" on it.. A knock out to mount the transformer to as seen below.

Also, is it better to hook to hot or cold water line?
How many gallons flow through in a cold day with the furnace running?
How much water should my humidifier use?
The amount of water that a humidifier uses depends on the type of humidifier.
A flow through humidifier (HE220/HE250 will use about three gallons of water per hour of operation. One half to three quarters of a gallon will be evaporated per hour to condition the air, while the rest flows down the humidifier pad. As it does so, the water flushes mineral deposits down the drain, thereby allowing longer service intervals between pad replacement.
#3
Member
Thread Starter
Join Date: Nov 2008
Location: Iowa
Posts: 4
Received 0 Votes
on
0 Posts
Thanks!
I have everything installed and running! I have a question on the operation of the humidifier though.
1. Do most people put the furnace fan on 'auto' - meaning that the humidifier only runs when the furnace kicks on which probably means the humidity level in the house is not as much as it could be, especially in newer better insulated homes. Or
2. Set the fan 'ON' and run the humidifier all the time - more energy and water - better humidity?
3. Also, I noticed that for water to even flow through the humidifier when the blower is running the humidistat seems to have to be slightly above 40. Is this normal or should I keep experimenting and see what setting works best?
Thanks
I have everything installed and running! I have a question on the operation of the humidifier though.
1. Do most people put the furnace fan on 'auto' - meaning that the humidifier only runs when the furnace kicks on which probably means the humidity level in the house is not as much as it could be, especially in newer better insulated homes. Or
2. Set the fan 'ON' and run the humidifier all the time - more energy and water - better humidity?
3. Also, I noticed that for water to even flow through the humidifier when the blower is running the humidistat seems to have to be slightly above 40. Is this normal or should I keep experimenting and see what setting works best?
Thanks
#4
Member
Thread Starter
Join Date: Nov 2008
Location: Iowa
Posts: 4
Received 0 Votes
on
0 Posts
OK, I am really second guessing myself now. The Honeywell 220 installation instructions show mounting the humidifier above the furnace - hot air side and the bypass damper to the cold air return. Now I see a bunch of stuff online and from other brands that the ideal mounting is just the opposite!
What's really right?
Do I need to switch this thing around to work efficiently and why the contradictions?? Arrgh!
Thanks
What's really right?
Do I need to switch this thing around to work efficiently and why the contradictions?? Arrgh!
Thanks
#5
You are welcome, glad to hear it's up and running.
I had mine wired up to EAC instead of HUM the first winter I had it, and I seen that the humidifier ran more with fan (more wasted water), and last year switched it over to HUM to only run with the heat, and it kept up just fine, less water is wasted.. They work better with hot air going over the pad. so leave the Humidifer to run with heat only.
I have variable speed, so I run my fan 24/7 in the heating seasons, and AUTO in the cooling season.
The HUM wire will only power up on call of heat, EAC will power any time the blower is running.
I run mine at 40%, and if the house is above 40%, it won't run. As you can see on the chart, the colder it gets, you should lower the % if you have frost building up on the windows.
No need to second guess yourself. Either side works just fine.. Not sure why Honeywell only shows it on the supply. I have mine on the return side, and it works just fine..
The air flow will always come from the supply side to the return, so the pad is always going to have hot air going over it.
Lot of pro perfer the unit on the return, just in case if there is water problem, you won't have to worry about damage to control or anything on the furnace itself.
1. Do most people put the furnace fan on 'auto' - Or
2. Set the fan 'ON' and run the humidifier all the time -
2. Set the fan 'ON' and run the humidifier all the time -
I have variable speed, so I run my fan 24/7 in the heating seasons, and AUTO in the cooling season.
The HUM wire will only power up on call of heat, EAC will power any time the blower is running.
3. Also, I noticed that for water to even flow through the humidifier when the blower is running the humidistat seems to have to be slightly above 40. Is this normal or should I keep experimenting and see what setting works best?
OK, I am really second guessing myself now. The Honeywell 220 installation instructions show mounting the humidifier above the furnace - hot air side and the bypass damper to the cold air return. Now I see a bunch of stuff online and from other brands that the ideal mounting is just the opposite!
What's really right?
What's really right?
The air flow will always come from the supply side to the return, so the pad is always going to have hot air going over it.
Lot of pro perfer the unit on the return, just in case if there is water problem, you won't have to worry about damage to control or anything on the furnace itself.
#8
Member
Join Date: Dec 2008
Location: new york metro
Posts: 10
Received 0 Votes
on
0 Posts

Jay - are you still out there?
I can't find that HUM wire and so currently I have mine wired directly from the 120 power going into my heating unit (ICECO) to the transfomer and then to the humdistat
I have a EAC on the motherboard of the HVAC but no wire coming out of it.
Another issue is that I have a small apartment without any return ducts - the bottom of the HVAC just has a filter so I was thinking of running the bypass down to that directly. Do you think that will work? I know Honeywell makes one with out a bypass but it won't fit in my small space.
THANK YOU SO MUCH for any info and help
I can't find that HUM wire and so currently I have mine wired directly from the 120 power going into my heating unit (ICECO) to the transfomer and then to the humdistat
I have a EAC on the motherboard of the HVAC but no wire coming out of it.
Another issue is that I have a small apartment without any return ducts - the bottom of the HVAC just has a filter so I was thinking of running the bypass down to that directly. Do you think that will work? I know Honeywell makes one with out a bypass but it won't fit in my small space.
THANK YOU SO MUCH for any info and help
#9
Yepper!
Are you using the sail switch, or nothing?
Is it a 1/4" male spade? If so, you can buy the 1/4" female spade to slide over that.
Into the cabinet, or is the furnace sitting on a duct/box?
I can't find that HUM wire and so currently I have mine wired directly from the 120 power going into my heating unit (ICECO) to the transfomer and then to the humdistat
I have a EAC on the motherboard of the HVAC but no wire coming out of it.
Another issue is that I have a small apartment without any return ducts - the bottom of the HVAC just has a filter so I was thinking of running the bypass down to that directly. Do you think that will work?
#10
Member
Join Date: Dec 2008
Location: new york metro
Posts: 10
Received 0 Votes
on
0 Posts
honeywell install
That is great - thank you so much for the quick response
I was using nothing but I just bought the kit with the sail switch
It is a 1/4" male
I think it is going directly into the cabinet
Are you using the sail switch, or nothing?...
Is it a 1/4" male spade? If so, you can buy the 1/4" female spade to slide over that...
Into the cabinet, or is the furnace sitting on a duct/box?...
Last edited by Jay11J; 12-03-08 at 09:47 AM. Reason: Fixed quotes.
#11
The sail switch won't be needed if you wire it to the furnace.
You can put it on to the side where a return would of been hooked up if it was in a home with return ductworks.
If you can take a photo of your set up, and we can be sure what you got going on.
FYI, to do a quote, you highlight the area you want quoted, and then click on the button above "Quote" button
I think it is going directly into the cabinet
If you can take a photo of your set up, and we can be sure what you got going on.
FYI, to do a quote, you highlight the area you want quoted, and then click on the button above "Quote" button
#12
Member
Join Date: Dec 2008
Location: new york metro
Posts: 10
Received 0 Votes
on
0 Posts
honeywell install
If I do not need the sail switch - should I be doing something different with my wires?
I also tried inserting pictures but it wants a URL address of the photo that is on my hardrive
I also tried inserting pictures but it wants a URL address of the photo that is on my hardrive

#13
I also tried inserting pictures but it wants a URL address of the photo that is on my hardrive

then you copy the URL/direct link to photo, and then past it on on where it asked you for the URl
#15
Is there room on the right side of the furnace?
how is the air getting to the air filter? (BTW, Air filter is over due for a change)
Is there gas water heater in the same area?
how is the air getting to the air filter? (BTW, Air filter is over due for a change)
Is there gas water heater in the same area?
#16
Member
Join Date: Dec 2008
Location: new york metro
Posts: 10
Received 0 Votes
on
0 Posts
honeywell install
Is there room on the right side of the furnace?
no there is a wall that is my bedroom closet
how is the air getting to the air filter? (BTW, Air filter is over due for a change)
the door to the closet is a louver door and there is a bout a 15 inchs from the wall to the unit (funny that you say that - I bought a filter today!)
Is there gas water heater in the same area?
no there is a wall that is my bedroom closet
how is the air getting to the air filter? (BTW, Air filter is over due for a change)
the door to the closet is a louver door and there is a bout a 15 inchs from the wall to the unit (funny that you say that - I bought a filter today!)
Is there gas water heater in the same area?
#17
Not a good thing to have this return pulling air out of the room that has two gas fired applainces.. Risk of CO.
I am not sure how we are going to tie the bypass into the return... Guess have a pipe go right down infront of the filter..
How did you get back there and cut the hole into the duct?
I am not sure how we are going to tie the bypass into the return... Guess have a pipe go right down infront of the filter..
How did you get back there and cut the hole into the duct?
#18
Member
Join Date: Dec 2008
Location: new york metro
Posts: 10
Received 0 Votes
on
0 Posts
honeywell install
I am not sure how we are going to tie the bypass into the return... Guess have a pipe go right down infront of the filter..
How did you get back there and cut the hole into the duct?
PS - I can take a higher res photo of motherboard if that is handy for you...
Last edited by Jay11J; 12-04-08 at 08:01 AM. Reason: fixed quote.
#20
That what I was thinking but I was worried about creating enough suction
I would use the flex/foil type, that way if it's in the way, it can easly be moved if needed.
#23
Member
Join Date: Dec 2008
Location: new york metro
Posts: 10
Received 0 Votes
on
0 Posts
honeywell install
I just want to make sure I understand...
I will take 12 gauge wire use only the one line (hot no neutral) get a spade, hook it up to the EAC (thats were I am going to get my power) and then go into transformer...but when I get to transformer it wants hot and a neutral - what should I do then?
I can't thank you enough for all the help and insight you have given me - thank you.
I will take 12 gauge wire use only the one line (hot no neutral) get a spade, hook it up to the EAC (thats were I am going to get my power) and then go into transformer...but when I get to transformer it wants hot and a neutral - what should I do then?
I can't thank you enough for all the help and insight you have given me - thank you.
#25
Member
Join Date: Dec 2008
Location: new york metro
Posts: 10
Received 0 Votes
on
0 Posts
Problem solved
Hi Jay - I just wanted to let you know that the wiring worked perfectly and I just have to wait and see if my makeshift duct work is working. I can't thank you enough!!!
#27
Member
Join Date: Jan 2009
Posts: 1
Received 0 Votes
on
0 Posts
Jay...
New guy...not even sure how to post. I have just installed a 6 gallon TrueSteam with IAQ. I really believe it was working fine the first day...once I saw the "set 10 to 1 and 25 to 2....but now it just never turns off. It runs the fan and shows the Hum light on the true steam even when the IAQ show the Humidity MUCH higher that the setting on the IAQ...any ideas...tia.
New guy...not even sure how to post. I have just installed a 6 gallon TrueSteam with IAQ. I really believe it was working fine the first day...once I saw the "set 10 to 1 and 25 to 2....but now it just never turns off. It runs the fan and shows the Hum light on the true steam even when the IAQ show the Humidity MUCH higher that the setting on the IAQ...any ideas...tia.
#29
Member
Join Date: May 2010
Location: Candad
Posts: 4
Received 0 Votes
on
0 Posts
Hello, I have similar problem after I installed a new furnace and a Honeywell HE225 humidifier. Water only supply to the humidifier when the heat kicks in. Though I have the FAN switched to ON all the time, but if heat not kicked in, no water supply to the humidifier. Therefore, my house humidity is always around 26% or below. As for my skins problem, I need at least 35% humidity. Will a Sail Switch or a Sensing Relay solve my problem? Thanks.
#30
Hello, I have similar problem after I installed a new furnace and a Honeywell HE225 humidifier. Water only supply to the humidifier when the heat kicks in. Though I have the FAN switched to ON all the time, but if heat not kicked in, no water supply to the humidifier. Therefore, my house humidity is always around 26% or below. As for my skins problem, I need at least 35% humidity. Will a Sail Switch or a Sensing Relay solve my problem? Thanks.