Installing Aprilaire 500A / 500M Humdifier on Lennox G12Q3-110-4
#1
Member
Thread Starter
Join Date: Jan 2009
Location: Chicago
Posts: 21
Received 0 Votes
on
0 Posts
Installing Aprilaire 500A / 500M Humdifier on Lennox G12Q3-110-4
All,
I live in the midwest and I am getting tired of feeling extra cold due to the lack of humidity plus the static electricity is terrible. To make a long story short, this Lennox furnace originally had a humidifier but it was removed when an air conditioner unit was installed a few years back. The furnace should probably be replaced but there are no funds in the budget at this time. Besides it has been given a clean bill of health from a recent inspection. My thoughts are to purchase a hunidifier now and reuse it when the furnace is replaced.
I am interested in either installing an Aprilaire 500A or 500M humidifier but have a few questions.
1) Can I install the bypass 6" duct opening on the supply which is located on the right side? My main concern is that the cooling coil is located right beneath the old 6" duct opening that was sealed up when the A/C was installed. If I do this the new 6" duct opening would just fit above the old hole under the vertical section of ducting but would be above the cooling coil. Should I be concerned with air flow to the bypass duct?
2) Assuming I am able to install either a 500A or 500M will I need a current sensing relay with either of the two units or just the 500M with my furnace?
3) Does anyone know if the 500A comes with the outside temperature sensor that is referenced or does it need to be purchased separatley? Also, is this ODT optional or required for the 500A to work?
Thanks all!
I live in the midwest and I am getting tired of feeling extra cold due to the lack of humidity plus the static electricity is terrible. To make a long story short, this Lennox furnace originally had a humidifier but it was removed when an air conditioner unit was installed a few years back. The furnace should probably be replaced but there are no funds in the budget at this time. Besides it has been given a clean bill of health from a recent inspection. My thoughts are to purchase a hunidifier now and reuse it when the furnace is replaced.
I am interested in either installing an Aprilaire 500A or 500M humidifier but have a few questions.
1) Can I install the bypass 6" duct opening on the supply which is located on the right side? My main concern is that the cooling coil is located right beneath the old 6" duct opening that was sealed up when the A/C was installed. If I do this the new 6" duct opening would just fit above the old hole under the vertical section of ducting but would be above the cooling coil. Should I be concerned with air flow to the bypass duct?
2) Assuming I am able to install either a 500A or 500M will I need a current sensing relay with either of the two units or just the 500M with my furnace?
3) Does anyone know if the 500A comes with the outside temperature sensor that is referenced or does it need to be purchased separatley? Also, is this ODT optional or required for the 500A to work?
Thanks all!

#2
yes, you can put a humidifier back on the furnace.
Is there anything controls or transformer left from the old one? I see the humidistat is still there.
As for the bypass you could put it in the duct that is going towards the right, that way we don't have to worry about the A-Coil being in the way.
Is there anything controls or transformer left from the old one? I see the humidistat is still there.
As for the bypass you could put it in the duct that is going towards the right, that way we don't have to worry about the A-Coil being in the way.
#3
Member
Thread Starter
Join Date: Jan 2009
Location: Chicago
Posts: 21
Received 0 Votes
on
0 Posts
As far as old hardware is concerned I believe the only thing left is the humidistat. I took a look in the blower motor area and I did not see any type of current sensing relay unless I missed it. Not sure if it is only required for 500M model only.
The duct on the right only goes to one section of the house, wouldn't that be an issue?
The duct on the right only goes to one section of the house, wouldn't that be an issue?
#4
The duct on the right only goes to one section of the house, wouldn't that be an issue?
#5
Member
Thread Starter
Join Date: Jan 2009
Location: Chicago
Posts: 21
Received 0 Votes
on
0 Posts
Thanks.
With the price difference aside, is there any reason why I would want to choose one unit or the other? That is the 500M vs the 500A?
Will I need to purchase an outside temperature sensor if going with the 500A?
With the price difference aside, is there any reason why I would want to choose one unit or the other? That is the 500M vs the 500A?
Will I need to purchase an outside temperature sensor if going with the 500A?
#6
I think I like the Automatic one over the manual dial for people in the northern states that has temps up and down pretty much everyday.
The 500A will come with an outdoor sensor and also a manual mode if you wish not to use the outdoor sensor.
I have the outdoor sensor on my Honeywell, and like it alot, I don't have to play with the dial when the temps drops down to -20˚ later this week.
The 500A will come with an outdoor sensor and also a manual mode if you wish not to use the outdoor sensor.
I have the outdoor sensor on my Honeywell, and like it alot, I don't have to play with the dial when the temps drops down to -20˚ later this week.
#7
Member
Thread Starter
Join Date: Jan 2009
Location: Chicago
Posts: 21
Received 0 Votes
on
0 Posts
Thanks. I think I am getting closer to pulling the trigger. Had a few other questions though?
You said the 500A comes with the outdoor temperature sensor. Will I need any additional wiring so I can connect it from the outside location to the humidifier? I'm also curious to what this thing looks like?
Also, the furnace is nearest to the West side of the house. Assuming I put the sensor on the brick surface outside it would be in my neighbor's gangway. I'm wondering how high I need to mount this thing to avoid the neighbor's kids from playing with it considering when it comes out from the basement wall since it will be well within reach of anyway outside the house. My guess is to mount it up a few feet higher on the wall so that it is out of general reach. Not sure how delicate this thing is.
Additionally, do you have any suggestions on how or what tool I would use to cut the 6" round hole for bypass?
Regarding, current sensing relay. Would I need the 24V (Aprilaire Model # 50) or 120V (Aprilaire Model # 51)? My guess is the 120V one.
thanks
You said the 500A comes with the outdoor temperature sensor. Will I need any additional wiring so I can connect it from the outside location to the humidifier? I'm also curious to what this thing looks like?
Also, the furnace is nearest to the West side of the house. Assuming I put the sensor on the brick surface outside it would be in my neighbor's gangway. I'm wondering how high I need to mount this thing to avoid the neighbor's kids from playing with it considering when it comes out from the basement wall since it will be well within reach of anyway outside the house. My guess is to mount it up a few feet higher on the wall so that it is out of general reach. Not sure how delicate this thing is.
Additionally, do you have any suggestions on how or what tool I would use to cut the 6" round hole for bypass?
Regarding, current sensing relay. Would I need the 24V (Aprilaire Model # 50) or 120V (Aprilaire Model # 51)? My guess is the 120V one.
thanks
Last edited by zguy23; 01-14-09 at 11:17 AM.
#8

Also, the furnace is nearest to the West side of the house. Assuming I put the sensor on the brick surface outside
Additionally, do you have any suggestions on how or what tool I would use to cut the 6" round hole for bypass?
Regarding, current sensing relay. Would I need the 24V (Aprilaire Model # 50)
#9
Member
Thread Starter
Join Date: Jan 2009
Location: Chicago
Posts: 21
Received 0 Votes
on
0 Posts
No, the back of the house is the yard side which has the A/C unit, electric meter and a porch which is open underneath. The problem (if it is one) is that the back of the house faces south. The porch itself is covered so the deck surface and underneath is shielded from the majority of rain, snow and sun.
#11
Member
Thread Starter
Join Date: Jan 2009
Location: Chicago
Posts: 21
Received 0 Votes
on
0 Posts
Thanks.
I will be draining the 500A into a Little Giant Condensate pump that is being used for the A/C unit. Is there a concern with using this pump with the humidifier?
Little Giant Pump Company - Model VCMA-15ULS
I will be draining the 500A into a Little Giant Condensate pump that is being used for the A/C unit. Is there a concern with using this pump with the humidifier?
Little Giant Pump Company - Model VCMA-15ULS
#17
Member
Thread Starter
Join Date: Jan 2009
Location: Chicago
Posts: 21
Received 0 Votes
on
0 Posts
Ok. Btw, I went and checked the 400A as an alternative. It is obviously more expensive but would eliminate the drain issue. The problem is it has a height 15-3/4" vs 13" of the 500A. I only have about 16" of vertical height so the 400A looks like it could fit but it would be real tight.
#20
Member
Thread Starter
Join Date: Jan 2009
Location: Chicago
Posts: 21
Received 0 Votes
on
0 Posts
Well, I received the humidifier the other day and started installing it yesterday.
It took a lot longer than I expected but I took my time with mounting it and making cuts.
I am almost done with the expection of the following:
- Mounting the temperature sensor (currently running in manual mode)
- Clean up the wiriing with zip ties, etc.
- Position the drain line better with respect to the condensation pump.
I do have a few questions still...
1) I mounted the humidistat controller on the nearest return duct but it is the smallest of the two mains. This one only gets air from one bedroom. Any concerns with leaving it here?
2) I used Tstat wire to power the humidistat. I will also use the same wiring to connect the outside sensor. I did not use this type of wiriing to connect the circuit coming from the H terminals to the water valve, current sensing relay and condensation pump. I used some 16 guage stranded wire to do this instead. I figured I would be wasting a lot of Tstat wire only to be utilizing one wire inside the cable itself since this whole circuit is in serial.
Any concerns with doing this?
3) I am very pleased with the outcome of the installation of the unit itself and the bypass ducting however I am not to thrilled with the messe wiriing. I know I could tact wiriing along joists if necessary but in this case the wires are running up and over the unit so things are just hanging all over the place.
What are my options here? Do I just use zip ties where possible and duct tape where wires are hanging around the humidifier and humidistat?
4) For the drain going to the condensation pump, does this need to be tied into a fixed piece of pvc like that was done by the A/C guys or can I just leave it as is but zip tie it so the hose does not pop out?
Some other general observations...
- The humistat controller always says it is ON regardless of the furnace or fan actually being on. The only way it will go off is if I turn it off, lower the manual setting or the humidity has reached to appropraite level. I believe this is do the wiriing required to support the current sensing relay and the fact that I had to jumper the terminals W/G and Cf to R and C respectively. I believe the only thing the humidstat relies on to turn on and off is its relative humidity readings since the water is being controlled by the current sensing relay regardless. Is that correct?
- I also turned off the water panel indicator by adjusting the dial as suggested in the instructions. Not a big deal but I guess we can not rely on the idiot light for advice on when to do so.
Here are some pictures...


It took a lot longer than I expected but I took my time with mounting it and making cuts.
I am almost done with the expection of the following:
- Mounting the temperature sensor (currently running in manual mode)
- Clean up the wiriing with zip ties, etc.
- Position the drain line better with respect to the condensation pump.
I do have a few questions still...
1) I mounted the humidistat controller on the nearest return duct but it is the smallest of the two mains. This one only gets air from one bedroom. Any concerns with leaving it here?
2) I used Tstat wire to power the humidistat. I will also use the same wiring to connect the outside sensor. I did not use this type of wiriing to connect the circuit coming from the H terminals to the water valve, current sensing relay and condensation pump. I used some 16 guage stranded wire to do this instead. I figured I would be wasting a lot of Tstat wire only to be utilizing one wire inside the cable itself since this whole circuit is in serial.
Any concerns with doing this?
3) I am very pleased with the outcome of the installation of the unit itself and the bypass ducting however I am not to thrilled with the messe wiriing. I know I could tact wiriing along joists if necessary but in this case the wires are running up and over the unit so things are just hanging all over the place.
What are my options here? Do I just use zip ties where possible and duct tape where wires are hanging around the humidifier and humidistat?
4) For the drain going to the condensation pump, does this need to be tied into a fixed piece of pvc like that was done by the A/C guys or can I just leave it as is but zip tie it so the hose does not pop out?
Some other general observations...
- The humistat controller always says it is ON regardless of the furnace or fan actually being on. The only way it will go off is if I turn it off, lower the manual setting or the humidity has reached to appropraite level. I believe this is do the wiriing required to support the current sensing relay and the fact that I had to jumper the terminals W/G and Cf to R and C respectively. I believe the only thing the humidstat relies on to turn on and off is its relative humidity readings since the water is being controlled by the current sensing relay regardless. Is that correct?
- I also turned off the water panel indicator by adjusting the dial as suggested in the instructions. Not a big deal but I guess we can not rely on the idiot light for advice on when to do so.
Here are some pictures...



#21
2) I used some 16 guage stranded wire to do this instead. I figured I would be wasting a lot of Tstat wire only to be utilizing one wire inside the cable itself since this whole circuit is in serial.
Any concerns with doing this?
Any concerns with doing this?
3) I am not to thrilled with the messe wiriing.
4) For the drain going to the condensation pump, does this need to be tied into a fixed piece of pvc like that was done by the A/C guys or can I just leave it as is but zip tie it so the hose does not pop out?
Do get it away from the hot flue pipe.
Some other general observations...
- The humistat controller always says it is ON regardless of the furnace or fan actually being on.
- The humistat controller always says it is ON regardless of the furnace or fan actually being on.
#22
Member
Thread Starter
Join Date: Jan 2009
Location: Chicago
Posts: 21
Received 0 Votes
on
0 Posts
Would there be an advantage of going this route? Would the humidifier be off if wired this way when the fan / furnace is not running? I wired it exactly as the manual indicated but would like to do it a better way. I also wonder what the terminals R, C W/G and Cf imply or mean in the heating world.
#23
Here is how I'd do it.

Would there be an advantage of going this route? Would the humidifier be off if wired this way when the fan / furnace is not running?
I also wonder what the terminals R, C W/G and Cf imply or mean in the heating world.
C= Common
This is for the display reading.
W/G= power for the water valve.
Cf= Common side of the valve.
H= is hook up for the humidifier.
#24
Member
Thread Starter
Join Date: Jan 2009
Location: Chicago
Posts: 21
Received 0 Votes
on
0 Posts
Jay,
Sorry for the delayed post but I have been out of town for business for the past few weeks.
Well I rewired as you suggested and it is no longer working.
The furnace has terminals R, W, Y, G, and T so I wired R and C of humidistat to R and W of the furnace. There is no C on this furnace.
Now the humidifier goes on when the furnace is not running and the display completely turns off when the furnace turns on.
Please advise.
Sorry for the delayed post but I have been out of town for business for the past few weeks.
Well I rewired as you suggested and it is no longer working.
The furnace has terminals R, W, Y, G, and T so I wired R and C of humidistat to R and W of the furnace. There is no C on this furnace.
Now the humidifier goes on when the furnace is not running and the display completely turns off when the furnace turns on.
Please advise.
#27
Ok, the the A/C wire that comes in from the unit outside, where are the attached to? One should be Y, and I am guessing the other one is on T?
This is an older furnace, and I am not able to pull anything up on it.
This is an older furnace, and I am not able to pull anything up on it.
#30
Member
Thread Starter
Join Date: Jan 2009
Location: Chicago
Posts: 21
Received 0 Votes
on
0 Posts
Ok. I did that Jay. Now I have another problem. The humidifier wants to run all the time along with the water valve obviously. I checked the circuit coming from the current sensing relay and it is always hot. Did the current sensing relay get fried?
#32
Member
Thread Starter
Join Date: Jan 2009
Location: Chicago
Posts: 21
Received 0 Votes
on
0 Posts
Yes it does stop when I disconnect the relay.
It looks identical to your diagram except that the relay is swapped with the pump since it is closest to the transformer. So transformer, relay, pump then humidistat terminals W/G and Cf.
I did a simple test by connecting a A/C volt meter as follows and it is always reading ~30V.
It looks identical to your diagram except that the relay is swapped with the pump since it is closest to the transformer. So transformer, relay, pump then humidistat terminals W/G and Cf.
I did a simple test by connecting a A/C volt meter as follows and it is always reading ~30V.

#34
Member
Thread Starter
Join Date: Jan 2009
Location: Chicago
Posts: 21
Received 0 Votes
on
0 Posts
Out of the transformer is the same. About ~30.00 VAC. Btw, I have two transformers available to me. One that came with the unit and one that was already installed on the furnace but not used. Both read within 29.98 VAC to 30.05 VAC. I am using the one supplied with the unit.
No, when I disconnect it from the blower wire, that is leave it hanging on the side it does not stop. Voltage is still seen across terminals W/g and Cf.
No, when I disconnect it from the blower wire, that is leave it hanging on the side it does not stop. Voltage is still seen across terminals W/g and Cf.
#36
Member
Thread Starter
Join Date: Jan 2009
Location: Chicago
Posts: 21
Received 0 Votes
on
0 Posts
That was my thought as well.
Am I stuck purchasing one of these online or can I get one locally?
Btw, I noticed that the control unit turns off completely when the lower door if the furnace is removed now. Is that normal?
Also, since the unit is still being controlled by the relay via the blower the idiot light will still be on regardless of whether the furnace is off or on.
Am I stuck purchasing one of these online or can I get one locally?
Btw, I noticed that the control unit turns off completely when the lower door if the furnace is removed now. Is that normal?
Also, since the unit is still being controlled by the relay via the blower the idiot light will still be on regardless of whether the furnace is off or on.
#37
If this is brand new, I'd go back to the dealer who you got this from. Otherwise, I've never seen them sold at retail stores.
Yes, the blower door switch is killing the power.
[/quote]Also, since the unit is still being controlled by the relay via the blower the idiot light will still be on regardless of whether the furnace is off or on.[/QUOTE]
The light? You mean the display light or call for humidity?
Btw, I noticed that the control unit turns off completely when the lower door if the furnace is removed now. Is that normal?
[/quote]Also, since the unit is still being controlled by the relay via the blower the idiot light will still be on regardless of whether the furnace is off or on.[/QUOTE]
The light? You mean the display light or call for humidity?
#38
Member
Thread Starter
Join Date: Jan 2009
Location: Chicago
Posts: 21
Received 0 Votes
on
0 Posts
Light, meaning, the call for humidity or the "humidifier on" light which is why I believe we tried to re-wire it in the first place. Oh well, I can chalk this up to a learning experience.
When I get the new relay I will go back to the original wiring as suggested by Aprilaire so that the display doesn't go dead when removing the door or changing the filter.
When I get the new relay I will go back to the original wiring as suggested by Aprilaire so that the display doesn't go dead when removing the door or changing the filter.