TrueSTEAM Install issue w/service light
#1
Member
Thread Starter
Join Date: Jan 2010
Location: Illinois
Posts: 5
Received 0 Votes
on
0 Posts
TrueSTEAM Install issue w/service light
I just installed my TrueSTEAM 12 gal humidifier with the Vision Pro IAQ thermostat with EIM on my single stage HVAC system. The thermostat and HVAC system work perfectly together as well as the outside temperature gauge is working correctly. My problem is with the TrueSTEAM...The service light flashes 7 times after I hit the "go" button to initiate steam production.
The installation manual I have and followed is 69-2285EF which can be found here under the literature tab: Honeywell Air Cleaners, Commercial & Residential Filtration Systems & Purifiers. -TrueSTEAM Humidification System
According to the manual, the 7 flashes denotes that the HVAC power is not present which is not the case since everything is working properly except for the TrueSTEAM. The TrueSTEAM is plugged into a dedicated 20A circuit, so that shouldn't be a problem.
Because I want the fan delay option turned on, I wired everything according to the diagram on page 21 of the installation manual ("Option 3: VisinPRO IAQ Wiring with Fan Delay" at the top of the page). DIP 4 is down and the installer setup #0374 is set to 3. I think the problem is with the R wires but I'm not sure. Inside the TrueSTEAM the R terminal is factory jumped with the RT terminal and inside the EIM the R terminal is factory jumped with both the RC & RH terminals. Should these jumpers be removed to clear this service error?
I would appreciate some direction on this matter before I start a trial and error method. Thanks!
The installation manual I have and followed is 69-2285EF which can be found here under the literature tab: Honeywell Air Cleaners, Commercial & Residential Filtration Systems & Purifiers. -TrueSTEAM Humidification System
According to the manual, the 7 flashes denotes that the HVAC power is not present which is not the case since everything is working properly except for the TrueSTEAM. The TrueSTEAM is plugged into a dedicated 20A circuit, so that shouldn't be a problem.
Because I want the fan delay option turned on, I wired everything according to the diagram on page 21 of the installation manual ("Option 3: VisinPRO IAQ Wiring with Fan Delay" at the top of the page). DIP 4 is down and the installer setup #0374 is set to 3. I think the problem is with the R wires but I'm not sure. Inside the TrueSTEAM the R terminal is factory jumped with the RT terminal and inside the EIM the R terminal is factory jumped with both the RC & RH terminals. Should these jumpers be removed to clear this service error?
I would appreciate some direction on this matter before I start a trial and error method. Thanks!
#5
Member
Thread Starter
Join Date: Jan 2010
Location: Illinois
Posts: 5
Received 0 Votes
on
0 Posts
The R wires aren't twisted together at the EIM but are snug in the terminal if that is what you meant. Testing across the R's and C of the EIM, I get 29V. When I tested the TrueSTEAM across the R & C terminals all I got was about 3V (there is no C wire hooked up on the TrueSTEAM per wiring diagram in original post).
#8
Member
Thread Starter
Join Date: Jan 2010
Location: Illinois
Posts: 5
Received 0 Votes
on
0 Posts

I'm finally a happy camper...your suggestion of hooking up the C wires between the EIM and TrueSTEAM was the answer!
I've looked through at least 3 different (current and older) versions of this installation manual and none of them had the C's being hooked up together between the EIM and TrueSTEAM.
I'm crossing my fingers that everything keeps working!
Thanks a bunch Jay!
I've looked through at least 3 different (current and older) versions of this installation manual and none of them had the C's being hooked up together between the EIM and TrueSTEAM.
I'm crossing my fingers that everything keeps working!
Thanks a bunch Jay!