Nest 2.0 & Honeywell HE250A

Hi, I'm trying to determine the proper way to hook up my Nest 2.0 to my Honeywell HE250A. Currently the HE250A is conected to a Honeywell Humidistat mounted on my duct. I understand I need to bypass the Humidistat... My HVAC guy stopped by for my annual service and I asked him about hooking it up. He said it's easy to do, handed me a White Rogers 90-380 relay and said run 2 wires to the Nest and the other 2 to the "HUM" control on the HE250A and you're done. I have no idea based upon the relay he gave me where to begin. Any help is appreciated!
 
  #2  
Old 12-16-12, 01:35 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
If you want to use the relay, then you wire that in place of the humidistat, then wire the coil side to Nest's * and C at the furnace.

Or redo the wires, and wire the Nest right to the humidifier itself, and no relay needed.

 
  #3  
Old 12-16-12, 01:48 PM
C
Member
Thread Starter
Join Date: Jul 2009
Location: Northeast, USA
Posts: 26
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks, Jay. So in my config, I don't need the relay and can connect the two wires from the humidistat directly to the Nest? Thanks.
 
  #4  
Old 12-16-12, 06:22 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
No, you will have to rewire it if you don't want to use the relay. You will undo the wire that is on the current t-stat since you are not using that power.
 
  #5  
Old 01-06-13, 04:59 AM
C
Member
Thread Starter
Join Date: Jul 2009
Location: Northeast, USA
Posts: 26
Upvotes: 0
Received 0 Upvotes on 0 Posts
Update

I had some time to look deeper at this.... On my humidifier there are two wires at the "hum control" that go to the humidistat. There is also a block inside the humidifier labeled "equip" which has GR and R that go into the furnace. Finally there is a 24v power block that also goes into the furnace.

Given this scenario, is there a different recommended way to hook up the nest?

Thanks!
 
  #6  
Old 01-06-13, 06:23 AM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ok, I found the diagram for this unit, and it's a newer model that I have not see in person.

You will need the relay for this.

So you wire the relay between the Nest * and C at the furnace.

Then the contact side of the relay, you will wire the HUM to it.
 
  #7  
Old 01-26-13, 05:11 AM
C
Member
Thread Starter
Join Date: Jul 2009
Location: Northeast, USA
Posts: 26
Upvotes: 0
Received 0 Upvotes on 0 Posts
Since the humidifier is already connected and fully functional (comes on independent of heat) does this change the config? The humidifier is already connected to "c" on furnace.
 
  #8  
Old 01-26-13, 06:15 AM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
I don't follow what you mean? Do you have the relay wired into place?
 
  #9  
Old 01-26-13, 06:28 AM
C
Member
Thread Starter
Join Date: Jul 2009
Location: Northeast, USA
Posts: 26
Upvotes: 0
Received 0 Upvotes on 0 Posts
I was checking the existing wiring and the humidfier is already connected to "c" on the furnace.
 
  #10  
Old 01-26-13, 06:43 AM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
You should have C and R from "Power" side of it to the furnace, and on the "Equipment" 'side there W and C also should be going to the furnace.

The relay coil side should be * and C. Relay contact side wired to "HUM/Control" on the humidifier

Dip switch on humidifier set "Monitor system" to on, and "call for fan" to off.
 
 