I just purchased the Aprilaire 400A humidifier with the model 60 control. I have a 30 year old Williamson Temp-O – Matic. Need help with wiring into furnace. Here is a schematic of the furnace.
 
Attached Images  
  #2  
Old 01-16-13, 06:08 AM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
What did you get with your order? (A50 relay or transformer)
 
  #3  
Old 01-16-13, 02:25 PM
P
Member
Thread Starter
Join Date: Jan 2013
Location: usa
Posts: 18
Upvotes: 0
Received 0 Upvotes on 0 Posts
Aprilaire 400A humidifier with the model 60 control wireing help

Aprilaire 400A humidifier with the model 60 control wireing help

Just the transformer
 
  #4  
Old 01-16-13, 06:11 PM
P
Member
Thread Starter
Join Date: Jan 2013
Location: usa
Posts: 18
Upvotes: 0
Received 0 Upvotes on 0 Posts
Question Aprilaire 400A humidifier with the model 60 control wireing help

I do not have the A50 current sensing relay. My neighbor is a pluming / heating contractor. He said to use a RIM 24V relay and wire it from the GF terminal of the model 60 controller to the blower motor. He explained that this way the furnace blower would come on not only when heat was being called for but also when just the humidity level is low. Will this work?
 
  #5  
Old 01-16-13, 06:52 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
Do you have A/C on your furnace?
 
  #6  
Old 01-16-13, 06:58 PM
P
Member
Thread Starter
Join Date: Jan 2013
Location: usa
Posts: 18
Upvotes: 0
Received 0 Upvotes on 0 Posts
[h=2]Aprilaire 400A humidifier with the model 60 control wireing help [/h]
No AC
 
  #7  
Old 01-16-13, 07:18 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
Do you have the "Fan Center" on your furnace?

If you don't then the Gf is not going to work. A50 relay then is needed.
 
  #8  
Old 01-17-13, 03:02 AM
P
Member
Thread Starter
Join Date: Jan 2013
Location: usa
Posts: 18
Upvotes: 0
Received 0 Upvotes on 0 Posts
Question Aprilaire 400A humidifier with the model 60 control wireing help

Not sure what you mean by fan center. I have attached a picture of my furnace wiring diagram.
 
  #9  
Old 01-17-13, 06:14 AM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
The diagram doesn't show it, but it can be added later on.
 
  #10  
Old 01-17-13, 01:25 PM
P
Member
Thread Starter
Join Date: Jan 2013
Location: usa
Posts: 18
Upvotes: 0
Received 0 Upvotes on 0 Posts
[h=2]Aprilaire 400A humidifier with the model 60 control wireing[/h]Is the same as a RIM relay my neighbor told me about? Can you explain what I need and how to wire it?
 
  #11  
Old 01-17-13, 08:13 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
I've never heard of "RIM" relay before?

I googled it and coming back with mixed results.

Take a photo of your furnace w/ the covers off..

The center would be on the left hand side in the burner section.
 
  #12  
Old 01-18-13, 03:20 AM
P
Member
Thread Starter
Join Date: Jan 2013
Location: usa
Posts: 18
Upvotes: 0
Received 0 Upvotes on 0 Posts
Question Aprilaire 400A humidifier with the model 60 control wireing help

Sorry, it's RIB not RIM. I'm pretty sure I don't have a fan center. Looks like just a junction box.
 
Attached Images  
  #13  
Old 01-18-13, 06:54 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ok, looks like you don't have it. (kinda dark on the left side of the photo)

I looked it up, and never seen such thing.. I'd suggest to do the fan center instead, and that will fit in place of the junction box cover. Then if you add A/C you are ready for it.
 
  #14  
Old 01-19-13, 05:03 AM
P
Member
Thread Starter
Join Date: Jan 2013
Location: usa
Posts: 18
Upvotes: 0
Received 0 Upvotes on 0 Posts
Aprilaire 400A humidifier with the model 60 control wireing help Read more: htt

Ok I can't attach any more file. Below is a link to the RIB web page that shows it.

http://ribrelays.com/images/product/...ets/RIBU1C.pdf
 
  #15  
Old 01-19-13, 05:30 AM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
I looked at those, and they are not the correct product.

Again, I'd suggest a fan center.
 
  #16  
Old 01-19-13, 06:19 AM
P
Member
Thread Starter
Join Date: Jan 2013
Location: usa
Posts: 18
Upvotes: 0
Received 0 Upvotes on 0 Posts
Question Aprilaire 400A humidifier with the model 60 control wireing help

Can you show me the correct wiring diagram and the correct fan center that I would use?
 
  #17  
Old 01-19-13, 06:44 AM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
I"m going off to work soon, I'll get back to you tonight, unless someone else here get to you before I do.
 
  #18  
Old 01-19-13, 08:09 PM
P
Member
Thread Starter
Join Date: Jan 2013
Location: usa
Posts: 18
Upvotes: 0
Received 0 Upvotes on 0 Posts
Question Fan center relay?

Still need help. Is the fan center relay a Packard FC90113 fan control center spdt relay?
[h=1][/h]
 
  #19  
Old 01-19-13, 08:25 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
I'm sorry not getting to you tonight. Friend stopped by and have to work in the am again.
 
  #20  
Old 01-20-13, 03:44 AM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes, the Packard FC90113 is one of the fan center that can work. One I was going to suggest is the Honeywell R8239B1076.

I won't do the wire detail till you got the model you are going for.
 
  #21  
Old 01-20-13, 07:08 AM
P
Member
Thread Starter
Join Date: Jan 2013
Location: usa
Posts: 18
Upvotes: 0
Received 0 Upvotes on 0 Posts
Question Aprilaire 400A humidifier with the model 60 control wireing help

Can you explain how the fan center relay works and what the letters mean?
 
  #22  
Old 01-20-13, 07:25 AM
P
Member
Thread Starter
Join Date: Jan 2013
Location: usa
Posts: 18
Upvotes: 0
Received 0 Upvotes on 0 Posts
The Honeywell is more expensive than the Packard and one is a DPDT vs SPDT. Whats the difference?
 
  #23  
Old 01-20-13, 08:02 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
What letters are you refering to?
 
  #24  
Old 01-21-13, 01:49 PM
P
Member
Thread Starter
Join Date: Jan 2013
Location: usa
Posts: 18
Upvotes: 0
Received 0 Upvotes on 0 Posts
Question

R, c, w, y , g ..............................................
 
  #25  
Old 01-21-13, 08:57 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
R = power
C = common
W = heat
Y = cooling
G = fan

[ATTACH=CONFIG]8179[/ATTACH]
 
Attached Images  
  #26  
Old 01-22-13, 01:28 PM
P
Member
Thread Starter
Join Date: Jan 2013
Location: usa
Posts: 18
Upvotes: 0
Received 0 Upvotes on 0 Posts
Question

Ok thanks for that. Which fan center do I need? I see them several ways. I have it the humidifier mounted. Can you show me the correct wiring for my furnace with the correct fan center?
 
  #27  
Old 01-22-13, 02:30 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
The SPDT is what you need for your furnace since the blower is only one speed.

Not sure if the color is going to be the same as other, so let me know what model you ordred, and will draw it out for you.
 
  #28  
Old 01-22-13, 07:05 PM
P
Member
Thread Starter
Join Date: Jan 2013
Location: usa
Posts: 18
Upvotes: 0
Received 0 Upvotes on 0 Posts
Question

I'm going to the pluming heating supply tomorrow but I really want to understand how this works. It seems wiring is different in many cases. On the model 60 control can you explain what each of the terminals do?
Power R &C. Why does it need two 24v power supply's?
Inputs ODT. I know this is the outdoor temp sensor.
W= call for heat. What does this mean?
G= Is this the 24v on the furnace from the thermostat? T1 and T2
H & H= Solenoid. Is this basically a switch turning the unit on and off?
GF= what does this do?
 
  #29  
Old 01-22-13, 08:53 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
R and C is for steady power for the humidistat to read humidity and display.
W let's the humidistat know there is call for heat to come on.
G is the input to know the fan is turned on from the t-stat.
H and H is the switch for the humidifier itself.
Gf is wired to the furnace (your case fan center) to turn on the fan if humidity is needed with out heat call.
 
  #30  
Old 01-23-13, 05:36 PM
P
Member
Thread Starter
Join Date: Jan 2013
Location: usa
Posts: 18
Upvotes: 0
Received 0 Upvotes on 0 Posts
Question

The Honeywell R8239B1076 is $60+ compaird to the White - Rogers for $20+. What is the differance? Can you show me the wireing for the white-Rogers?
 
  #31  
Old 01-23-13, 08:06 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
What model from White - Rogers? 90-113?
 
  #32  
Old 01-24-13, 01:33 PM
P
Member
Thread Starter
Join Date: Jan 2013
Location: usa
Posts: 18
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes the 90-113.............
 
  #33  
Old 01-24-13, 06:23 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ok, how to wire it. (I am not able to draw it, sorry!)
----------------------------
The black wire from transformer wired to the incoming hot wire that has wire nut black wire from fan limit control.

White wire from transformer to all white wires on wire nut.
-----------------------------
Relay side

Brown/N.C. wire from relay going to Red wire from fan center. (Undo red wire from fan)

Red/N.O. wire from relay going to incoming hot wire that has the transformer wired into.

Black/Common wire going to red wire from fan motor.

Hope this helps.
 
  #34  
Old 01-30-13, 05:54 PM
P
Member
Thread Starter
Join Date: Jan 2013
Location: usa
Posts: 18
Upvotes: 0
Received 0 Upvotes on 0 Posts
My neighbor installed the RIB relay to turn the blower on when there is a call for humity. At first I didn't think is was working. It came on along with the blower when in test, but when it was turned down enough to turn it off it didn't come on right away. It seems to have a delay. But so far its working. Thanks for the help.
 
  #35  
Old 01-30-13, 06:38 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the update, and glad to hear it's working. Have a great week!
 
 