Aprilaire 600 Humidifier

I am connecting an Aprilaire 600 Humidifier with Automatic Digital Humidistat to a Lennox G40UH furnace. I have the following wiring connections:

Humidistat (R) - 24V Transformer
Humidistat (C) - 24V Transformer
Humidistat (ODT) - Outdoor Temperature Sensor
Humidistat (W) - Furnace Heat (W)
Humidistat (G) - Thermostat Fan (G)
Humidistat (H) - Humidifier Solenoid
Humidistat (Gf) - Furnace Common (C)

I am having trouble getting power to the solenoid. I have 24V to the humidistat and 24V across W/G. When I turn the furnace fan and put the humidistat in test mode I do not have any voltage across humidistat (H) terminals which power the solenoid. I did test the solenoid with direct voltage and it appears to function properly. Does anyone have any tips or suggestions for wiring? Thank you in advance.
 
  #2  
Old 02-10-13, 01:21 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
REMOVE the Gf from C!!! Gf should be going to G on the furnace.

Do you have the a wire hooked up to the other H?

Where is the other wire from the humidifier going to?
 
  #3  
Old 02-10-13, 01:40 PM
2
Member
Thread Starter
Join Date: Feb 2013
Location: United States
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Jay, thank you for your response. I rerouted the Gf wire to the Furnace (G) but did not see any different response. I should have made it more clear in my initial post but both (H) wires are connected to the two wires from the solenoid. After approximately 30 seconds of test mode operation I receive an r1 error but cannot seem to find that explained anywhere.
 
  #4  
Old 02-10-13, 07:56 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
Only one wire from the humidifier goes to H other wire goes to C. Then should be power going to the other H.
 
  #5  
Old 02-11-13, 06:56 AM
2
Member
Thread Starter
Join Date: Feb 2013
Location: United States
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Jay, thank you for your input. I now have the humidistat wired exactly as the picture below:

http://i1206.photobucket.com/albums/...HUMIDISTAT.png

However, I am still having trouble with the solenoid turning on. The only way I can turn the solenoid on with the current wiring set up is to run the furnace, switch the blower activation (on humidistat controller) to the 'on' position, and turn the humidistat knob to test/reset. The solenoid will then click on and run on settings 4-7. As soon as I turn off the blower activation (on humidistat controller) the solenoid closes regardless if the blower is still running. Thank you.
 
Attached Images  
  #6  
Old 02-11-13, 08:52 PM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
When you set the switch to AUTO, the humidistat is calling for humidty, but the valve won't open unitill you switch the blower switch to ON?
 
  #7  
Old 02-12-13, 04:51 AM
2
Member
Thread Starter
Join Date: Feb 2013
Location: United States
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Yes, the only way I can turn it on is in test mode with the blower activation switch on. Even if the humidity is at 10-15% and on setting 7, it will not call for humidity or open the valve.
 
  #8  
Old 02-12-13, 05:57 AM
Jay11J's Avatar
Member
Join Date: Sep 2001
Location: Rochester, Minnesota
Posts: 16,984
Upvotes: 0
Received 0 Upvotes on 0 Posts
Make sure W is getting power when heat is on. If there is power them you may have a bad humidistat.
 
 