Nest - Solenoid on bypass humidifier not engaging - 16v output on *

Hi all, hoping someone can help.

I cannot get NEST to activate the solenoid. Heat, Cool, Fan all work fine.

I decided to measure the voltage for '*' from nest to 'C' on furnace terminal and get 16V. What do I need to do? Shouldn't nest be putting out 24V from '*"?
---
1. * (star) is connected to one end of the solenoid
2. Other end of the solenoid is connected to 'C' terminal at furnace.
3. 'C' is also run from the furnace to 'C' on nest.

Equipment:
1. Bypass Humidifier - 24v solenoid (U147112 - 24/60)
2. Furnace: Lennox G43UF. Terminals W C R G Y - all 24v
3. NEST

-vf
 
Sponsored Links
  #2  
Old 11-23-14, 08:01 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,244
Received 1,121 Votes on 1,041 Posts
Welcome to the forums.

I have seen some humidifiers draw too much current and drag the * output from the nest too low for the humidifier to work.

What is the input voltage at the nest when the * is at 16vac ?
If you disconnect the humidifier.... does the * voltage return to +/- 24vac ?

You may need to have the nest control a relay and then use the relay to operate the humidifier.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: