Honeywell 360 humidifier not working

Reply

  #1  
Old 01-14-15, 03:26 PM
R
Member
Thread Starter
Join Date: Jan 2015
Location: United States
Posts: 2
Received 0 Votes on 0 Posts
Honeywell 360 humidifier not working

I have a 5 year old unit that has worked fine over the years. I turned the humistat up until it 'clicked', opened the saddle valve. When the heater started, the sail was forced down and the solenoid 'clicked'. OK! No water. Checked the hose from the saddle valve to the solenoid by taking the fitting off and holding it over a bucket. Water! My unit uses a mounted AC to 24 volt power supply. Checked with a volt meter, 27 volts.
Am I correct in my assumption that the sail switch is just a normally open switch and there isn't any other electronics involved, correct?
Also, after trying this for approximately 5 minutes, the solenoid body was slightly warm indicating current flow.
Based on the above scenario, I bought another solenoid valve. Wired it in, same problem! Help!
Ronster9
 
Sponsored Links
  #2  
Old 01-14-15, 03:44 PM
R
Member
Thread Starter
Join Date: Jan 2015
Location: United States
Posts: 2
Received 0 Votes on 0 Posts
Honeywell 360 not working

PJMax,
Just read your suggestion on this thread about a bad humidistat being the problem. I will try that tomorrow morning. Sounds like it will do the trick. What is in the humidistat?



Separated from... http://www.doityourself.com/forum/hu...s-voltage.html
 

Last edited by PJmax; 01-14-15 at 09:11 PM.
  #3  
Old 01-14-15, 11:12 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,166
Received 1,114 Votes on 1,034 Posts
I combined your posts into your own thread. It's very confusing when a problem is spread into different threads.


A humidistat is just a single pole switch connected to a moisture sensing medium. The switch is small and light duty. Every time it opens it arcs from the solenoid opening. Over time the contacts get burned and no longer make contact.

You need to have your solenoid connected to power when checking the voltage right at the valve.

The humidistat and the sail switch are both nothing more than normally open switches. On a call for humidity..... the humidistat closes. When the blower starts.... the sail switch closes.
 

Last edited by PJmax; 01-15-15 at 12:02 AM.
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: