Aprilaire 600 new solenoid still not working

Reply

  #1  
Old 02-15-15, 08:43 AM
M
Member
Thread Starter
Join Date: Feb 2015
Location: Usa
Posts: 1
Received 0 Votes on 0 Posts
Aprilaire 600 new solenoid still not working

The Name:  image.jpg
Views: 518
Size:  40.6 KBName:  image.jpg
Views: 480
Size:  31.4 KB

24 v comes from the furnace board to the humidifier controller. I read 27v.

I separated the wires at the solenoid and read 26.9.

I replaced the solenoid as it was not opening figuring that was the issue yet I am still not getting water flow.

I assumed I could take the power supply right from the furnace and connect it to the valve, so I did and instant water flow. But I can't leave it that way

Can the issue be in the humidifier control board?

Any help?
 
Sponsored Links
  #2  
Old 02-15-15, 10:09 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,044
Received 1,105 Votes on 1,025 Posts
Welcome to the forums.

You need to check for 24vac on the solenoid with the wires connected. If you have 24vac to the controller but not to the solenoid.... the humidistat is defective.
 