400 series aprilaire humidifier not working

My aprilaire humidifier is not getting any water. It has a manual humidistat. I checked the voltage at the two connections on humidistat and it's around 24v with the furnace running. I get no voltage at the connection to the solenoid. I've already replaced the solenoid, thinking that was the problem. Any suggestions?
 
Sponsored Links
  #2  
Old 12-07-15, 03:55 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,098
Received 1,112 Votes on 1,032 Posts
Welcome to the forums.

When the humidistat calls for humidity..... the switch closes and you should read 0v across it. It sounds like it's not closing. You can short those two wires to test the humidifier.
 
  #3  
Old 12-09-15, 09:59 AM
R
Member
Thread Starter
Join Date: Dec 2015
Posts: 3
Received 0 Votes on 0 Posts
Which two wires? The ones connected to the humidistat?
 
  #4  
Old 12-09-15, 01:33 PM
R
Member
Thread Starter
Join Date: Dec 2015
Posts: 3
Received 0 Votes on 0 Posts
Figured it out, jumped the wires connected to the humidstat. Turned on furnace and solenoid turned on the water to humidifier. New humidistat on the way.
 
  #5  
Old 12-09-15, 06:40 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,098
Received 1,112 Votes on 1,032 Posts
Glad you figured it out. You should be all set with the new h'stat.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: