Aprilaire 700M and Armstrong Ultra 80 furnance

Greetings. I need some assistance with wiring my new humidifier. I have purchased an Aprilaire 700M and it is installed on a Armstrong Ultra 80 oil fired furnace. The furnace is approximately 25 years old.

I have completed all of the installation except for the wiring the humidistat and actual humidifier. I am not very good at reading schematics and am asking for detailed instructions to ensure I wire it correctly. I also have a transformer that came with the humidifer as well.

As a side note, I replaced an old Sears humidifier and it was wired directly to the fan blower motor. I understand that this will not work with the Aprilaire.

I have attached pictures of the furnace to provide a visual so hopefully someone can assist me. Thanks in advance.
Name:  082.jpg
Views: 1294
Size:  15.8 KBName:  084.jpg
Views: 4709
Size:  41.6 KBName:  085.jpg
Views: 6093
Size:  43.2 KBName:  086.jpg
Views: 1432
Size:  48.7 KBName:  087.jpg
Views: 1455
Size:  49.0 KBName:  088.jpg
Views: 1587
Size:  43.3 KBName:  089.jpg
Views: 1307
Size:  37.3 KBName:  090.jpg
Views: 2948
Size:  45.8 KB
 
  #2  
Old 02-17-16, 02:34 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,811
Received 3,740 Upvotes on 3,356 Posts
Welcome to the forums.

How was your Sears unit wired..... with a transformer ?

You have a basic heating system with no control board. The only way to connect your humidifier is to use a current sense relay like the model 50.

Aprilaire-50-Sensing-Relay-24-volt/dp/B002T0ZTNC
 
  #3  
Old 02-17-16, 04:31 PM
D
Member
Thread Starter
Join Date: Feb 2016
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
the Sears was connected directly with the blower motor. 110v as far as I know. Is there anyway to use the transformer that was included with it to connect it? thanks for the reply.
 
  #4  
Old 02-17-16, 05:54 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,811
Received 3,740 Upvotes on 3,356 Posts
You can connect the supplied transformer to the blower motor.

Otherwise you'll need to supply the new transformer with power and use the #50 switching relay.
 
  #5  
Old 02-17-16, 06:20 PM
D
Member
Thread Starter
Join Date: Feb 2016
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Ok, so i connect the hot and neutral from the blower to the transformer and then I hook the white and black from the transformer to what? Sorry if I am being too naive.
 
  #6  
Old 02-17-16, 06:46 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,811
Received 3,740 Upvotes on 3,356 Posts
No problem....

Since the wiring between the transformer, humidistat and humidifier is AC.... there is no polarity.

Name:  700M_copy.jpg
Views: 1757
Size:  21.3 KB
 
  #7  
Old 02-17-16, 07:26 PM
D
Member
Thread Starter
Join Date: Feb 2016
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Awesome. thanks for the drawing it really helps. I will connect it in the morning. Thanks again!
 
  #8  
Old 02-18-16, 07:16 AM
D
Member
Thread Starter
Join Date: Feb 2016
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Well that didn't work. Just burned up the transformer.
 
  #9  
Old 02-18-16, 09:55 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,811
Received 3,740 Upvotes on 3,356 Posts
The wiring diagram is correct. I'm not sure what happened there.
Was something shorted on the 24v side ?
 
  #10  
Old 02-18-16, 11:23 AM
D
Member
Thread Starter
Join Date: Feb 2016
Location: USA
Posts: 6
Upvotes: 0
Received 0 Upvotes on 0 Posts
Wired it per the diagram, and when the blower kicked on the transformer smoked and arced. Not sure what else to do.
 
  #11  
Old 02-18-16, 11:25 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,811
Received 3,740 Upvotes on 3,356 Posts
That sounds like the voltage was higher than 120v applied to the transformer. Usually an oil fired furnace will use a 120v blower motor but maybe yours is different. It will need to be checked.
 
 