Dehumidifier blows cold air and doesn't collect water

I have a Heat Controller model BHD-501-G that started blowing cold air, not collecting water, but the compressor gets super hot. I'm assuming that this might be worthless at this point, but any help you could give me would be much appreciated.
 
Sponsored Links
  #2  
Old 09-29-16, 03:46 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,146
Received 1,113 Votes on 1,033 Posts
Do you have good airflow out of the unit ?
Is the air coming out colder than the room temperature or the same ?

A dehumidifier is basically an air conditioner. The air enters the front thru a foam filter and contacts the cold evaporator. The humid air condenses on the evaporator coil and the condensate runs down to the catch pan. The air continues thru the unit and blows thru the condensor coil cooling the hot refrigerant and the compressor.
 
  #3  
Old 09-30-16, 10:17 AM
M
Member
Thread Starter
Join Date: Aug 2015
Location: United States
Posts: 7
Received 0 Votes on 0 Posts
The airflow, is great. It seems to be coming out slightly colder than room temperature. Filter is clean. I've got a fairly good knowledge of air conditioners, refrigerators, etc., which is why I'm kind of baffled here. There was never an leakage from the bottom. I use a multimeter and a lot of other tools regularly, but I'm not sure where to go from here...
 
  #4  
Old 09-30-16, 02:29 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,146
Received 1,113 Votes on 1,033 Posts
Remove the front panel and filter. Feel the evaporator coil.
If it's not ice cold you probably have a refrigerant leak.
 
  #5  
Old 09-30-16, 06:54 PM
M
Member
Thread Starter
Join Date: Aug 2015
Location: United States
Posts: 7
Received 0 Votes on 0 Posts
The copper line on the side that coils around 5 times and goes into the front coils is cold and condensing, but that's it. Actually, the "L" part is freezing. If you need pics, let me know, I'll have more time tomorrow.
 
  #6  
Old 09-30-16, 07:29 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,146
Received 1,113 Votes on 1,033 Posts
That sounds like the supply line to the coil.
If the line is getting cold but not the coil then it definitely sounds low on refrigerant.
Basically time for a new one.
 
  #7  
Old 10-01-16, 07:06 AM
M
Member
Thread Starter
Join Date: Aug 2015
Location: United States
Posts: 7
Received 0 Votes on 0 Posts
Yeah, I kind of figured. Luckily, it's actually my backup. Thanks a lot for the help! I'll visit and refer the site in the future.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: