Nest 3rd Gen + Aprilaire 500

Long story short the solenoid for my humidifier is not getting enough voltage to open. The way the wiring is set up is the wiring from the thermostat go to my zoning panel, HZ311, then to the furnace.

1. Across my power and common at the circuit board in the furnace I'm getting 28.55v
2. From my *, humidifier signal wire, to the common at the zoning panel I'm at 26.61v. The humidifier wire does not go to the panel. It gets jumped to the wiring that goes to the furnace.
3. Inside the furnace the voltage drops again to 23.5v, * to common
4. Once the fan activates voltage drops again to 22.6v and this is the same reading I get at the solenoid valve.

Do I need another transformer and a relay installed? Another question I have is why is there such a voltage drop across the lines? When the humidifier is "active" I still have 28.55v across the power and common.

Appreciate your input.
Thanks
 
Sponsored Links
  #2  
Old 11-16-17, 07:01 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 59,039
Received 1,104 Votes on 1,024 Posts
Welcome to the forums.

Not completely sure what you have there or how it's wired.

If the R and C power for the nest thermostat comes from a zoning board then one wire from the humidifier goes to C on the zoning board. The other humidifier wire goes to the * terminal. No connections to the furnace.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is On
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: