Honeywell HE240 and Ecobee
Pete-
I see this is a newish thread. I'm having an issue with my Honeywell HE240. I ran one wire from my control board common (24v) to the solenoid. The other wire went to the ACC+ of the Ecobee. Do I need the relay in this configuration? I guess I'm not entirely sure what the relay does. Thanks in advance!
I see this is a newish thread. I'm having an issue with my Honeywell HE240. I ran one wire from my control board common (24v) to the solenoid. The other wire went to the ACC+ of the Ecobee. Do I need the relay in this configuration? I guess I'm not entirely sure what the relay does. Thanks in advance!
Last edited by elpeejo; 01-02-18 at 12:12 PM.
#2
Welcome to the forums.
Take the two wires coming out of the HE240 and touch them together. If the humidifier starts you need a relay. That signifies a powered unit. A powered unit has its own built in 24vac control transformer. Yours should not be powered and the wiring you've stated should be fine.
Take the two wires coming out of the HE240 and touch them together. If the humidifier starts you need a relay. That signifies a powered unit. A powered unit has its own built in 24vac control transformer. Yours should not be powered and the wiring you've stated should be fine.
#3
Member
Thread Starter
Join Date: Jan 2018
Location: USA
Posts: 2
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Thanks! It is not powered, and I am running this set up instead of the supplied transformer. The issue is, when calling for a heat cycle, the solenoid clicks on and off rapidly for some time. It eventually stops, but can start up again. Everything else was working fine. I even had my house above 30% humidity in 0 degree weather. Overnight, it decided to quit working. I'm still not sure why the solenoid was doing that, and if that's the reason for failure.
Edit: I see now this particular thread is for powered humidifiers. Apologies. I'm scouring the web for anything as my humidity is now sitting at 17%. Not fun for me or the family!
Edit: I see now this particular thread is for powered humidifiers. Apologies. I'm scouring the web for anything as my humidity is now sitting at 17%. Not fun for me or the family!
#4
You'll notice this is your own thread now.
I believe the HE-240 has a pressure switch used to sense blower operation. You don't want that active. I'm thinking you want to connect directly to the solenoid wires without the pressure switch connected. The Ecobee will energize the ACC+ terminal when it determines humidity is needed and the furnace is in a call for heat.
I believe the HE-240 has a pressure switch used to sense blower operation. You don't want that active. I'm thinking you want to connect directly to the solenoid wires without the pressure switch connected. The Ecobee will energize the ACC+ terminal when it determines humidity is needed and the furnace is in a call for heat.