Aprilaire 600 to 500 swap not working


  #1  
Old 01-15-18, 04:35 PM
T
Member
Thread Starter
Join Date: Jan 2018
Location: United States
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Aprilaire 600 to 500 swap not working

Hello, I had an Aprilaire 600 that I was using in Manual Mode so when i needed a new humidifier I purchased another aprilaire thinking that since the wiring was done by a professional I could just swap the wires and be done. That doesn't seem to be the case. I purchased a new Aprilaire 500 digital and placed the wires in the same configuration except i ran the wire for the ODT so that I was not in manual mode any longer. I do not have the thermostat (ecobee4) running it though. Once i was completed i started the furnace (goodman installed 2011) and I put it in Test\Reset mode and no water released. I checked to make sure the Saddle Valve was open and plenty of water can run straight through but the when i connect it and run the test it does not trigger it to flow. PS i did just tonight add the old humidifier controller on and it will trigger it. I added the old wiring pic and the new wiring pic is there something else that needs connected for the digital controller? when do i need to use the transformer that was included

Name:  aprilaire_old.jpg
Views: 276
Size:  20.7 KBName:  aprilaire_new.jpg
Views: 373
Size:  96.7 KB
 
  #2  
Old 01-15-18, 06:44 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,063
Received 3,596 Upvotes on 3,225 Posts
The new humidistat wires/works a little differently. It's a better design.

Move the red solenoid wire to the R terminal. Add a short jumper from C to where the red solenoid wire was.
You have a three wire cable that supplies R and C. Use the green wire. Connect it to W on that h'stat and W on the furnace board. That should do it. The diagram illustrates the connections.

Name:  600A_T - Copy.JPG
Views: 1937
Size:  57.9 KB
 
  #3  
Old 01-16-18, 11:34 AM
T
Member
Thread Starter
Join Date: Jan 2018
Location: United States
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Pete that worked perfectly thanks. What did I do with the "W" cable though. why did i have to bring that from the furnace to the humidistat?
 
  #4  
Old 01-16-18, 01:44 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,063
Received 3,596 Upvotes on 3,225 Posts
On the new humidistat...W tells it to turn on.
 
 