GeneralAire 1042LH bypass humidifier to Ecobee 3.

Reply

  #1  
Old 02-27-18, 05:38 AM
Member
Thread Starter
Join Date: Feb 2018
Location: Canada
Posts: 11
GeneralAire 1042LH bypass humidifier to Ecobee 3.

Thanks to everyone for the detailed advice - I have read it all carefully and tried multiple suggestions but must be one small step from getting this to work. Hoping someone can point me in the right direction?

I have a GeneralAire Bypass Humidifier (1042LH) that I am trying to get running with my EcoBee 3. Worked fine hooked up to the old Humidistat which I have now bypassed. I tried to upload a wiring diagram but could not get it to work so I will quickly explain:

From the solenoid two identical black wires. One now runs to ACC+ on the ecobee and one to a terminal on a transformer before the furnace board. There is a second wire running to the other port on the transformer that runs to behind the ecobee but which I currently do not have attached to anything. From the transformer, one white wire runs to the HUM-N terminal on the furnace board a black wire runs to the EAC-N terminal. These connections from the transformer to the board were in place from when it was wired to the humidistat and I have not changed them.

Any suggestions?
Thanks!
Chris
 
Sponsored Links
  #2  
Old 02-27-18, 10:29 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: NJ - USA
Posts: 43,508
Look at the diagram below. One wire from the solenoid goes to ACC+ and the other solenoid wire goes to C at the furnace. That's it! There can be nothing else in line. Follow this diagram exactly.

Name:  bee.JPG
Views: 210
Size:  36.9 KB
 
  #3  
Old 02-27-18, 12:32 PM
Member
Thread Starter
Join Date: Feb 2018
Location: Canada
Posts: 11
Hi Pete
Thanks for the reply. Yes I actually went as far as to print out that diagram from your very first post before I asked my question. I made my changes based on that however .... the transformer threw me. To be clear you are saying just disconnect that, unplug both wires from the furnace board and set it aside, then simply hook that second humidifier wire to C? That simple?
Thanks again
Chris
 
  #4  
Old 02-27-18, 12:55 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: NJ - USA
Posts: 43,508
Yes... that is correct.

The reason for the transformer was that the HUM terminal on your furnace board is 120v. The transformer supplied switched 24vac to the humidistat and the humidifier. Now... the ecobee supplies that switched 24vac.
 
  #5  
Old 02-27-18, 05:11 PM
Member
Thread Starter
Join Date: Feb 2018
Location: Canada
Posts: 11
I should have added to my original post that I am using the PEK - which one of your posts below suggests will not support the humidifier connection. My bad for not spotting that before. Problem I now have is that I connected the other humidifier wire to C to try it and the ecobee briefly came on and has now gone black. I took the wire out again and rechecked everything was sat as before but no dice, ecobee is still black. Did I fry it? Not sure how I would have given the humidifier wire does not carry any power. Maybe I fried the PEK?

Since I have an extra wire behind the ecobee (1 was freed up from bypassing the humidistat that had two wires originally - so I now have 5 in total) could I reconfigure this to not require the PEK anyway or is the C wire different from the others since it is carry voltage?

Chris
 

Last edited by fossie_chris; 02-27-18 at 05:41 PM. Reason: Corrections
  #6  
Old 02-27-18, 05:56 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: NJ - USA
Posts: 43,508
Do you have a voltmeter ?
Check for 24vac at the R and C terminals on the furnace. You may have blown a control fuse on the furnace board. It will be a small plastic fuse. Usually 3-5A and look like a plastic automotive fuse.

The R is 24vac. If it was DC.... it would be the positive and the common is the negative. Only the thermostat electronics use the C connection. All the other functions are switched to R.
 
  #7  
Old 02-27-18, 06:54 PM
Member
Thread Starter
Join Date: Feb 2018
Location: Canada
Posts: 11
Ok, I can get hold of a voltmeter. No voltage means new fuse ... Hopefully that gets me back up and running.

What about repurposing the other wire behind the ecobee to be a common wire and get rid of the PEK? Would that work?
 
  #8  
Old 02-27-18, 08:07 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: NJ - USA
Posts: 43,508
Will you have enough wires to do what you want ?

You need R, C, ACC+, W, G and Y if you have A/C.
 
  #9  
Old 02-27-18, 08:15 PM
Member
Thread Starter
Join Date: Feb 2018
Location: Canada
Posts: 11
Yes in total I have six wires. Bypassing the old humidistat bought me two wires that run down to the furnace board already but are no longer used. One would have to go to ACC+ but it sounds like I could now repurpose the other one to be a C wire?
 
  #10  
Old 02-27-18, 08:25 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: NJ - USA
Posts: 43,508
Yes.... you can make that a C wire now.
 
  #11  
Old 02-27-18, 08:42 PM
Member
Thread Starter
Join Date: Feb 2018
Location: Canada
Posts: 11
First off major thanks - 1 50c 3A fuse later and everything is back up and running again! Letting the house warm up overnight and then I will try repurposing that C wire and seeing if the humidifier finally starts up.

Serious appreciation - thank you!
 
  #12  
Old 02-27-18, 09:33 PM
Member
Thread Starter
Join Date: Feb 2018
Location: Canada
Posts: 11
Hmm, so it doesn't like something about connecting the wire from the humidifier to the C terminal of the furnace board. I have now removed the PEK and repurposed a wire to be the C wire from the ecobee to the furnace. That all works great until I add in the humidifier wire to that C terminal. When I do that the ecobee starts up but reboots as soon as it gets to the home screen. It does that in an infinite loop. Removing the humidifier wire from C fixes the issue. Everything is now wired exactly as in your diagram. I'm stuck again.
 
  #13  
Old 02-28-18, 10:26 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: NJ - USA
Posts: 43,508
Did you program the ecobee for 1 wire acc operation ?

Ok.... try this for me..... connect the humidifier directly to the furnace board. Connect one solenoid wire to C and the other temporarily to R. The humidifier should begin and run. No call for heat is needed.

Does this work ?
 
  #14  
Old 02-28-18, 05:55 PM
Member
Thread Starter
Join Date: Feb 2018
Location: Canada
Posts: 11
Yes I did configure as a 1-wire accessory.

Tried what you suggested. Removed all other wires and just hooked up the humidifier wires from the solenoid to R and C. It immediately blew the 3A fuse again.
 
  #15  
Old 02-28-18, 08:10 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: NJ - USA
Posts: 43,508
Then you have a short between that point and your humidifier.
 

Last edited by PJmax; 03-01-18 at 08:32 PM. Reason: moved thread to new location
  #16  
Old 03-01-18, 07:28 PM
Member
Thread Starter
Join Date: Feb 2018
Location: Canada
Posts: 11
Thanks Pete. Since it keeps blowing the fuse, is there a way to test the humidifier without connecting it to the furnace board? I am thinking I should now be looking at replacing the wire from the solenoid or perhaps even the solenoid itself? The humidifier is quite simple so can't imagine what else to look at?
Chris
 
  #17  
Old 03-01-18, 08:34 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: NJ - USA
Posts: 43,508
I'd start by disconnecting the wiring at the solenoid. Using an ohmmeter check the two wires between the humidifier and the furnace for a short.

Check the solenoid for a short. It should measure probably better than 50 ohms.
 
  #18  
Old 03-04-18, 12:03 PM
Member
Thread Starter
Join Date: Feb 2018
Location: Canada
Posts: 11
Thanks. Just waiting to get hold of an ohmmeter and then I will post back.
 
  #19  
Old 03-12-18, 07:55 PM
Member
Thread Starter
Join Date: Feb 2018
Location: Canada
Posts: 11
OK, I have an ohmmeter (finally) but little idea how to use one ... you said disconnect the wires at the solenoid. Am I then positioning one of the rods at each end of the wire to measure for whether resistance is passing through the wire properly? How would I check the solenoid (where would I make my connection points?)
Thanks
 
  #20  
Old 03-12-18, 08:51 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: NJ - USA
Posts: 43,508
Set the meter to read low ohms.... or auto ohms. Disconnect the wires from the solenoid. Put one probe on each solenoid wire. What do you measure ?

With the wires disconnected from the solenoid...... go to the furnace.... disconnect the wires there. Check between the two wires. You should see no continuity.... no measurement.

Now.... touch one probe to something grounded..... furnace metal frame..... touch other probe to one wire. You should see no continuity. Now try with the other wire.
 