Nest 3.0 with Aprilaire 600

Hi, I'm new on these forums, and I've read a number of the posts on humidifiers with Nests. We recently purchased a house with a humidifier installed but unwired. I have wired a Nest thermostat to the furnace, which is a Lennox G60UHV(X), and wired the Aprilaire 600 humidifier to the Nest following the diagram below. Everything seems to be working correctly. I'm a little confused about the need for a relay though. I have a White Rogers 90-290Q relay on hand, would it hurt to add that in? Thanks for any help!

Matt

 
Sponsored Links
  #2  
Old 11-04-18, 09:48 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 46,256
Welcome to the forums.

Your installation is wired correctly.
A relay is only needed if your humidifier had its own built in 24vac transformer. Yours does not.
(keep the relay in stock for the future)
 