Wait 5000 humidifier & Goodman furnace

Hi folks,

Thank you in advance for reading my question.

I have the followings and want to connect them together.
- Wait 5000 Humidifier PDF manual
- Goodman furnace GMSS92 PDF manual
- White Rodgers thermostat 1F78 PDF manual

My furnace and thermostat are already wired for heat/cool on 4 wires for a single transformer system (Figure 4 on page 3 of the thermostat's manual). The cable between the furnace and the thermalstat has 5 wires. So there is one wire not currently used.

The problem is that my humidifier is already installed too high up, leaving no room for installing the humidistat.

Sheet metal work is a pain for me. Instead of relocating the humidifier to a lower height to make room for installing the humidistat, I would much prefer to install the humidistat next to the thermalstat in the living room, IF POSSIBLE.

So my question is: given my scenario, is it possible to connect the humidifier to the furnace and install the humidistat next to the thermalstat in the living room using the existing cable of 5 wires?

I tried the following loop of wire, but blew the 3A fuse on the furnace control board.
- Connected RH on the thermalstat to terminal 1 on the humidistat
- Connected terminal 2 on the humidistat to the unused wire.
- Connected the other end of the unused wire (at the furnace now) to one of the 24 VAC IN on the humidifier
- Connected the other 24 VAC IN on the humidifier to W on the furnace control board.

Thanks again.
 

Last edited by PJmax; 05-19-20 at 08:54 AM. Reason: fixed links
Sponsored Links
  #2  
Old 05-19-20, 08:58 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 56,343
Received 741 Votes on 696 Posts
Welcome to the forums.

You would connect one of the humidifier wires to C on the furnace board.
Connect your spare stat wire to the other humidifier wire.

At the thermostat..... connect W from the stat to one humidistat terminal.
Connect the spare wire to the other humidistat terminal.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are Off
[IMG] code is On
HTML code is On
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: