Aprilaire 500 wiring to new heat pump & oil furnace.


  #1  
Old 11-19-23, 11:39 AM
D
Member
Thread Starter
Join Date: Nov 2023
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Aprilaire 500 wiring to new heat pump & oil furnace.

Installed a Gree heat pump and am trying to hook up aprilaire 500m with model 60 humidifier control. Furnace is a tempstar amp105-ie2 oil furnace with oil being backup heat. Current thermo is a honeywell rth7600d. I cannot figure the wiring out. Can i just tie into reversing valve (b/0) instead of using W. W- should only work if I'm in emergency heat. Also customer (my wife) wants hot water to humidifier. Is this a must....? its a very long run.
 

Last edited by Dancram; 11-19-23 at 01:01 PM.
  #2  
Old 11-21-23, 01:30 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,843
Received 3,748 Upvotes on 3,361 Posts
Welcome to the forums.

We keep a single topic in one thread. This is your thread.

You can get your R and C from the fan center.
You can't use the reversing valve line is that is always active when in heating mode.

The easiest thing to do is to get the Aprilaire A-50 controller.
Aprilaire A-50 on special

The blower motor neutral wire runs thru the metal clip on the A-50.
When the blower runs.... it turns on and activates the humidifier.
If you didn't want to set the transformer... you could get solenoid power from R and C terminals.


Unfortunately you do not get the most effective humidity output from a heat pump system with cold water. Hot water is definitely more effective. A long hot water line is not helpful either. Humidifiers don't use a lot of water so by the time the hot water reached the humidifier it would be shutting off. It would require insulating the line if hot water is used.
 
  #3  
Old 11-23-23, 03:22 AM
D
Member
Thread Starter
Join Date: Nov 2023
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the input. A tech told me to wire it to G instead of white and keep the fan on auto and in the summer turn off the controller, will that work as well? I am trying that today. I am running the hot water line....and insulating. I hope that helps a little.
 
  #4  
Old 11-23-23, 09:05 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 63,843
Received 3,748 Upvotes on 3,361 Posts
G can't be used in dual fuel setups.
The heat pump will activate the G terminal but the oil furnace will not.
G is typically a faster blower speed than required for a fossil furnace.
 
 