Romex wiring gague

Can I connect 12/2 to existing 14/2 in a run for additional recessed lighting fixtures?
 
Sponsored Links
  #2  
Old 12-05-10, 10:32 AM
W
Join Date: Dec 2005
Location: USA
Posts: 3,188
Received 0 Votes on 0 Posts
Nope. You can't mix wire gauge in a circuit.
 
  #3  
Old 12-05-10, 11:08 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 13,605
Received 204 Votes on 181 Posts
Originally Posted by Wayne Mitchell View Post
Nope. You can't mix wire gauge in a circuit.
You may use larger wire to an existing circuit but this is frowned upon as it just causes confusion later.
 
  #4  
Old 12-05-10, 11:41 AM
B
Member
Thread Starter
Join Date: Dec 2010
Location: USA
Posts: 2
Received 0 Votes on 0 Posts
Thanks! I was just wondering because I have aleft over box of 12/2 and wanted to make sure adding 2 lights to the existing 14/2 circut wasn't against code.
 
  #5  
Old 12-05-10, 01:48 PM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 39,967
Received 5 Votes on 5 Posts
Advice given so far is right on. You can't mix the wiring, large to small. This, of course, brings up a parody. Using a 20 amp circuit and 12 gauge wire to a light fixture, and inside the fixture you connect your 12 gauge wire to a 16 gauge stranded wire. Just goes against the grain.
 
  #6  
Old 12-05-10, 07:05 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: Twin Cities, MN
Posts: 13,605
Received 204 Votes on 181 Posts
Originally Posted by chandler View Post
Using a 20 amp circuit and 12 gauge wire to a light fixture, and inside the fixture you connect your 12 gauge wire to a 16 gauge stranded wire.
The difference is the fixture wire is, many times, a higher temp rating then the THHN/NM-b wire. Also, it only needs to carry the current for the light itself and not the current of the entire circuit. This is covered in Art. 402 (2005)
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: