Temp Rated wiring questions for new fixtures
Old 11-30-11, 02:06 PM
D
This was partially covered in a older, but still relevant for my project. I'm installing a pair of 90 C. temprature rating florescent lights in a bathroom redo. My question is, if I leave the existing 60 temp wire up to the wall switch then run new 90 C wire from the wall/Dimmer switch to the pair of lights (appx 4 '). Is that sufficient or do I need to provide a length of (new) wire in front of the switch? If so how much? Would it be beneficial to use armored cable from the dimmer to the fixtures ?
Thanks
Dan
Old 11-30-11, 02:09 PM
pcboss's Avatar
Received 194 Upvotes on 170 Posts
You could just rewire from the switch to the dimmer.
Armored cable is more expensive and harder for a homeowner to work with for little advantage.
Old 11-30-11, 04:27 PM
D
Thanks for the quick response.
To clarify, the circuit is as follows: main breaker panel -> wall switch -> light. I'm planning on replacing the wall switch with a dimmer switch so the circuit will become : main breaker panel -> dimmer switch -> pair of lights.
Thanks
Dan
Old 11-30-11, 08:03 PM
pcboss's Avatar
Sounds fine.
Now would be the time to install new circuits while the walls are open.
Old 12-01-11, 06:22 AM
D
Just so I'm clear, The main panel is in a different part of the house, only the bathroom walls are exposed. I'm not planing to alter the incoming (older) wire (from main) to the dimmer switch. Only replacing the wire from the dimmer switch to the fixtures.
I'm assuming the reason to do this is due to the potential for greater heat build up in the wires (due to higher amp?) associated with the new fixtures up to the dimmer switch. But the heat buildup isn't going to travel past the dimmer switch (towards the main)?? I guess I'm not clear on how far the heat will travel.
Thanks
Dan
Old 12-01-11, 01:02 PM
F
The increased heat is from the lamp itself. It is NOT a problem with the current flow through the wiring UNLESS that current flow exceeds 15 amperes on a #14 conductor or exceeds 20 amperes on a #12 conductor.
Old 12-01-11, 02:05 PM
Gunguy45's Avatar
Super Moderator
Received 6 Upvotes on 6 Posts
Don't mean to hijack here or anything...but this makes me wonder.
Since they are legislating for lower energy consumption in bulbs...which translates to less heat (esp with LED and CFL bulbs), why the requirement for higher temp insulation on the wires?
Old 12-02-11, 06:30 AM
D
Guys thanks for the info (probably meant ballast not lamp as these are fluorescent lights) . I suspect the higher temp rating is due to the ballast energy/heat which would likely be hidden in the wall or surrounding insulation. Energy/heat given off by lamps will be transmitted to surrounding rooms increasing to some extent increased energy costs.
Old 12-02-11, 09:29 AM
ray2047's Avatar
Ballasts are never hidden in the wall.
Old 12-02-11, 10:01 AM
pcboss's Avatar
This was to combat the effect of the Easy-Bake oven the heat of the bulbs was slowly cooking the life out of the insulation. After the abuse the insulation would crack and fall off the conductors.