dimmer switch voltage readings

I've installed a lutron dimmer switch for a ceiling fixture (fixture not yet installed) and i'm getting a voltage reading at the point of use of 32 when the switch is off and 98 when the switch is on. is this low reading typical for dimmers? with a regular switch installed i get the usual 0 when switch is off and 119 when switch is on.
thanks.
 
Sponsored Links
  #2  
Old 12-29-11, 03:41 AM
chandler's Avatar
Banned. Rule And/Or Policy Violation
Join Date: Dec 2005
Location: USA
Posts: 39,965
Received 6 Votes on 6 Posts
You are getting "phantom" voltage reading from a digital meter, which is normal. Get an analog meter and the readings will be accurate. Is this a 3 way set up? where are you touching your probes? You should be using line to neutral or ground.
 
  #3  
Old 12-29-11, 03:50 AM
GregH's Avatar
Super Moderator
Join Date: Jan 2001
Location: Manitoba
Posts: 10,134
Received 37 Votes on 35 Posts
Try setting your meter to direct current.
Most dimmers output a modified sine wave and play havoc with digital meters which is why chandler's suggestion is a good one.

Also, some dimmers don't have an actual switch for the off position and may bleed some voltage when in the "off position.
 
  #4  
Old 12-29-11, 08:21 AM
W
Member
Thread Starter
Join Date: Feb 2010
Location: usa
Posts: 14
Received 0 Votes on 0 Posts
thanks for the responses guys...
It's a single pole setup, and i'm taking the reading between line and neutral. I will try a dc reading and report back.
 
Reply
Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Thread Tools
Search this Thread
 
Ask a Question
Question Title:
Description:
Your question will be posted in: