Linking LED under cabinet lighting.
Old 11-15-13, 09:33 PM
B
What kind of wire should be used to link 8 "LED light under cabinet lighting" in parallel? Each fixture is 12 watts for a total of 88 watts. The desire is to hardwire with a single switch.
Old 11-16-13, 04:34 AM
ray2047's Avatar
Received 13 Votes on 11 Posts
What is the voltage? Are they each 120 volts?
Old 11-16-13, 08:47 AM
B
Yes, they are each 120 volt.
Old 11-16-13, 08:53 AM
ray2047's Avatar
Then you would need to use protected NM-b (AKA Romex) or metallic cable (AKA BX). If this is a kitchen the lights can not be on the countertop receptacle circuit. If the breaker is 15 amp you would use #14. If the breaker is 20 amp #12.
Old 11-16-13, 09:00 AM
B
Smile
The circuit is a 15-amp. Are there other variations of 14-gauge wire that maybe more practical under the cabinets? That is, THW, THWN, THHN, XHHW-2, etc...?
Old 11-16-13, 10:03 AM
ray2047's Avatar
Those are all individual conductors and must be used in a raceway such as conduit or surface raceway (AKA Wiremold).
Old 11-17-13, 09:49 PM
B
Smile
Ok, thank you for your information. Have a great week.