Siemens Circuit/Panel breakers rating.

I have SIEMENS G4040MB1200 panel breaker installed in home. When I look it up online and on label I find that it is 200-Amp load center. When I calculate total AMP from each breaker TOTAL comes to 580 AMP. Am I missing/miscalculating something?

Does this mean that – if 5 breakers with 40 AMP rating trips then it will cut off the MAIN?
 

Last edited by NewHO2013; 11-17-13 at 01:08 PM.
  #2  
Old 11-17-13, 11:53 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Northern NJ - USA
Posts: 61,440
Received 1,410 Votes on 1,304 Posts
When you calculate load on a panel you need to add up devices...... not circuit breaker size.

You have a 20 amp breaker for the kitchen but nothing is on.... no load there. So you can't count that circuit as an automatic 20amp load.

What you do need to do is make sure your 200amp service is big enough for all your large loads.
Make a list of big loads..... like electric heat, electric cooking, electric cooling, electric hot water heating.
 
  #3  
Old 11-17-13, 01:32 PM
F
Member
Join Date: Mar 2006
Location: Wet side of Washington state.
Posts: 18,495
Received 36 Votes on 28 Posts
I have in excess of 800 amperes worth of circuit breakers on my 200 ampere main circuit breaker. I seriously doubt that I have ever pulled in excess of 50 amperes total on my service.
 
 