Linking undercounter xenon lights


  #1  
Old 04-28-14, 06:47 PM
B
Member
Thread Starter
Join Date: Apr 2014
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Linking undercounter xenon lights

Currently have four xenon lights hard wired to a switch and linked together. 15 bulbs total 18 watts each. Each light has a 60 watt transformer, model
#WH-601E6-3. No light manufacturer marking on the lights. How many lights can I link together. Some xenon lights can link 600 total watts.
 
  #2  
Old 04-29-14, 06:30 AM
P
Temporarily Suspended
Join Date: Jul 2008
Location: NY
Posts: 10,265
Upvotes: 0
Received 0 Upvotes on 0 Posts
What else is on that circuit?
 
  #3  
Old 04-29-14, 12:15 PM
B
Member
Thread Starter
Join Date: Apr 2014
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Three other wall outlets. The only thing used on the outlets is a toaster in the morning. Lights are usually on only at night.
 
  #4  
Old 04-29-14, 12:25 PM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Three other wall outlets. The only thing used on the outlets is a toaster
That would make it an SABC. Only receptacles can be on that circuit. If the lights are hard wired they need to be on a separate. circuit.
 
 