Bathroom Vanity Lighting w/ multiple Fixtures


  #1  
Old 08-27-14, 09:38 AM
C
Member
Thread Starter
Join Date: Oct 2012
Location: United States
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
Bathroom Vanity Lighting w/ multiple Fixtures

Hello.
I am replacing my bathroom vanity light fixture and need a bit of help. There is one electrical box in the wall centered over the mirror. The old vanity light fixture was this type (oops sorry...the old fixture picture is sideways but you can still see it).

The new fixture is similar in that I built a long rectangular wooden box which I plan to mount 5 individual single light fixtures to. My question is since I only have the one electrical box in the wall with one set of wires how to I 'attach' with wires each individual fixture so it becomes one cohesive fixture unit?

Thanks

I've attached a picture of the white fixture box I built. I've mounted one of the lights on it. I need to mount and wire 4 more exactly like that one...two on each side for a total of five. How should I wire them together?

Name:  20140403_134619.jpg
Views: 605
Size:  26.1 KB

Name:  b.jpg
Views: 1246
Size:  18.1 KB
 

Last edited by ray2047; 08-27-14 at 10:51 AM. Reason: Rotate image.
  #2  
Old 08-27-14, 10:54 AM
ray2047's Avatar
Member
Join Date: Mar 2006
Location: USA
Posts: 29,711
Upvotes: 0
Received 15 Upvotes on 13 Posts
Not sure I understand the question. The wires from each fixture would be connected to the power in cable.
 
  #3  
Old 08-27-14, 03:41 PM
C
Member
Thread Starter
Join Date: Oct 2012
Location: United States
Posts: 7
Upvotes: 0
Received 0 Upvotes on 0 Posts
Sorry. I'll try to clarify. Each fixture has its own black and white. The spacing between the fixtures is too far for the wires from one fixture to reach the next. How should I bridge that gap? 14/2?

Thanks
 
  #4  
Old 08-27-14, 04:08 PM
P
Temporarily Suspended
Join Date: Jul 2008
Location: NY
Posts: 10,265
Upvotes: 0
Received 0 Upvotes on 0 Posts
14/2 would be the correct gauge. However, I don't know if that's a good idea. Aren't there any fixtures available that don't require all that extra wiring?
 
  #5  
Old 08-27-14, 04:32 PM
J
Member
Join Date: Jul 2014
Location: usa
Posts: 258
Upvotes: 0
Received 0 Upvotes on 0 Posts
Sorry. I'll try to clarify. Each fixture has its own black and white. The spacing between the fixtures is too far for the wires from one fixture to reach the next. How should I bridge that gap? 14/2?

Thanks
14-2 wg NM is great

get a round box for each fixture

maybe a hole saw to cut the hole
 
  #6  
Old 08-27-14, 05:53 PM
Handyone's Avatar
Member
Join Date: Aug 2000
Location: U.S.
Posts: 4,807
Upvotes: 0
Received 0 Upvotes on 0 Posts
I think I understand your question. You want to use the "white fixture box" as a path to easily run cable between the additional fixtures, thereby avoiding drilling through studs, etc.
I will let one of the electricians comment on this. I just wanted to comment to bring attention to it.
Each outlet box should be in the wall, and each fixture's wiring should be contained in a wiring box.
The "white fixture box" does not serve as conduit.
 
  #7  
Old 08-27-14, 08:53 PM
J
Member
Join Date: Jul 2014
Location: usa
Posts: 258
Upvotes: 0
Received 0 Upvotes on 0 Posts
The "white fixture box" does not serve as conduit.
RIGHT.....................i would call it the wall
OR
i would call it a soffit
or
i would call it a very nice place to hide the wire going from box to box
 
  #8  
Old 08-28-14, 12:26 AM
pcboss's Avatar
Forum Topic Moderator
Join Date: Jul 2002
Location: Maryland
Posts: 13,976
Received 194 Upvotes on 170 Posts
RIGHT.....................i would call it the wall
OR
i would call it a soffit
or
i would call it a very nice place to hide the wire going from box to box
And none of those are a listed means to contain a splice as required by the NEC. A box with suitable space is needed behind each fixture with suitable wiring means between boxes.
 
 