Can I power 30,000 watts of lighting off of a 3 phase 100 amp panel? Commercial space has 208volt.
 
  #2  
Old 09-03-14, 02:19 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,481
Received 913 Upvotes on 771 Posts
Welcome to the forums!

That would be about 83 amps of lighting. A little more than the 80% rule and that's if everything is balanced perfectly. Doesn't give you any room for anything else. How did you come to the 30KW number?
 
  #3  
Old 09-04-14, 06:20 AM
J
Member
Join Date: Jul 2014
Location: usa
Posts: 258
Upvotes: 0
Received 0 Upvotes on 0 Posts
Can I power 30,000 watts of lighting off of a 3 phase 100 amp panel?

does each leg have 110 volts to ground?
no 208 hi-leg in the mix?
 
  #4  
Old 09-04-14, 06:28 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,481
Received 913 Upvotes on 771 Posts
does each leg have 110 volts to ground
It will likely be 120 to ground, nominal.
OP also posted it as a 208v system, so it is likely a Wye, unless he was measuring from the high leg to ground.
 
  #5  
Old 09-04-14, 07:52 AM
S
Member
Join Date: Mar 2009
Location: United States
Posts: 459
Upvotes: 0
Received 0 Upvotes on 0 Posts
You said about 83A. How many watts would that allow for? A little over 17kW?
 
 