Wire outlet between switch and light

Reply

  #1  
Old 10-10-14, 09:15 AM
Member
Thread Starter
Join Date: Oct 2014
Posts: 1
Received 0 Votes on 0 Posts
Wire outlet between switch and light

This seems really simple but I can't get it to work. Power comes into the overhead light which runs to a switch. All wired with 14-2. I want to put an outlet between the switch and the light that is powered all the time. Do I need to run 14-3 instead of the 14-2 that's there already? Thanks for any help you can provide.
 
Sponsored Links
  #2  
Old 10-10-14, 09:53 AM
ray2047's Avatar
Group Moderator
Join Date: Mar 2006
Location: USA
Posts: 33,597
Received 13 Votes on 11 Posts
Won't work you don't have a neutral. the white wire is not a neutral. Yes, you need to change to 14-3 (or 12-3 if 20 amp breaker). The red and black will be your switch loop. Traditionally black will be your constant hot to receptacle and switch. Red will be switched hot back to the light. Under 2011 NEC the neutral can't stop at the receptacle. It must continue on to the light and be capped off for future possible use if not needed.
 
Reply