This is a Code question.
Can I daisy-chain wiring flourescent fixtures?
In other words... running a feed into a fixture, splice, and wiring out to another fixture.
Can I splice within a fixture, or, do I have to run each fixture to a source feed such as a 1900 box?
 
  #2  
Old 10-20-16, 06:30 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 14,405
Received 896 Upvotes on 757 Posts
Yes. It is done all the time. The only caveat is any wires within 3 inches of the ballast will need to be rated 90 degrees. The good news is any THHN, MC, or NM-b cable will have 90 degree wire.
 
  #3  
Old 10-20-16, 07:30 PM
B
Member
Thread Starter
Join Date: Oct 2010
Location: USA
Posts: 92
Received 0 Upvotes on 0 Posts
What wire type is used in Romex?

What wire type is used in Romex?
 
  #4  
Old 10-20-16, 07:41 PM
C
Member
Join Date: May 2015
Location: USA
Posts: 3,187
Received 175 Upvotes on 143 Posts
The original Type NM romex had 60 Deg C wire. It has been replaced by type NM-B romex that has 90 deg C rated conductors. I think it was the 1984 electrical code that started requiring NM-B.
 
 