Detached garage wiring

So my question is I have a 20 amp breaker feeding my detach garage. It comes in on 12/2 to a receptacle thatís for the garage opener then splits off to 14/2 on 2 light fixtures should I change those to 12/2 for those light fixtures because I wanted to add another receptacle.
 
  #2  
Old 04-23-18, 04:01 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 65,108
Received 3,986 Upvotes on 3,578 Posts
Welcome to the forums.

If the circuit is protected at 20A using the #12 wiring...... then all connected wiring also needs to be #12.
 
  #3  
Old 04-23-18, 08:49 PM
I
Member
Thread Starter
Join Date: Apr 2018
Posts: 2
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks I ended up replacing the 14 with 12 fun fun
 