Replacing light switch
Im replacing my light switch with a sensor occupancy switch but there are so many extra wires with the current switch. My old switch has 3 blacks 2are screwed on and 1 is connected to the switch) a red connected to the swtich and the ground is screwed on in the back of the box. All the 3 whites are capped. New switch has 2 blacks, green and bare grounds. Not sure which blacks go??





Last edited by PJmax; 07-07-19 at 03:41 PM. Reason: imported pics from links
#2
Welcome to the forums.
Photobucket no longer allows third party linking so your pictures were not available to all members to see. They are now stored here in your attachment folder.
Take all three black wires from the switch and connect them together. Those three will connect to one sensor switch wire. LINE if it is labeled. The red wire goes to the other sensor wire. LOAD if it's labeled.
Since the wiring is romex.... there should be a bare neutral in the box you can connect the green to.
Photobucket no longer allows third party linking so your pictures were not available to all members to see. They are now stored here in your attachment folder.
Take all three black wires from the switch and connect them together. Those three will connect to one sensor switch wire. LINE if it is labeled. The red wire goes to the other sensor wire. LOAD if it's labeled.
Since the wiring is romex.... there should be a bare neutral in the box you can connect the green to.
#3
Member
Thread Starter
Join Date: Jul 2019
Posts: 4
Upvotes: 0
Received 0 Upvotes
on
0 Posts
Not sure I follow. Which black on the new switch would connect to the old 3 black also what does the 2nd black on the new switch connect to? I don't understand what I do with the red? Wouldnt I just cap the red and not use it?
#7
Since there is no neutral wire needed for that switch...... it uses the lamp load to obtain power.
It will have a specific requirement for the lamp load which is typically 40 watts minimum.
It will have a specific requirement for the lamp load which is typically 40 watts minimum.