Outdoor Wiring

Reply

  #1  
Old 08-13-19, 11:15 AM
B
Member
Thread Starter
Join Date: Nov 2001
Location: usa
Posts: 528
Received 1 Vote on 1 Post
Outdoor Wiring

If I wish to run a line outdoors please clarify what is typically required regarding:

1. UF Cable - Must it be buried? If not in conduit how deep? Can it be unburied if not in conduit? If in conduit what kind of conduit? (plastic/rigid metal, etc) Does the type of conduit effect its burial depth? Is this standard or vary depending on your municipality?

Thanks
 
  #2  
Old 08-13-19, 12:11 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,796
Received 307 Votes on 263 Posts
In conduit 18" deep.
If no conduit 24" deep.
If it comes above ground it should be protected by conduit where it enters and exits the ground.
PVC electrical conduit is fine.
 
 