Need help
How’s everyone doing I need a se count opinion on this job I got customer wants to wire a room separate to his house that’s about 100-200 ft away from his house he wants 8 plus 3 switches and 3 lights and wants to install an a/c unit in there also I’ve talked to him and told him the best way to go is to instal a 100amp sub panel and run #6 wire with it, he keeps telling me there a better way to do it withought needing a sub panel but to my understanding that would be the best option
or can someone else give me another opinion thanks
or can someone else give me another opinion thanks
#2
Welcome to the forums.
That's considered a separate building from the house. You can call it a room or a shed or a garage. The code allows one circuit of power connected to it. That means you will need a sub panel in there along with a ground rod. You could set a 60A sub panel on those #6's. You may get some light flickering when the A/C cycles as that's a fairly long run. A 240v AC would perform better. Don't forget you'll need four wires as that is a sub panel.
That's considered a separate building from the house. You can call it a room or a shed or a garage. The code allows one circuit of power connected to it. That means you will need a sub panel in there along with a ground rod. You could set a 60A sub panel on those #6's. You may get some light flickering when the A/C cycles as that's a fairly long run. A 240v AC would perform better. Don't forget you'll need four wires as that is a sub panel.