Outdoor Wiring


  #1  
Old 03-20-20, 05:40 AM
B
Member
Thread Starter
Join Date: Nov 2001
Location: usa
Posts: 548
Received 2 Upvotes on 2 Posts
Outdoor Wiring

Can you bury THW wire in rigid PVC conduit to a depth of only 12" if GFCI protected? I was told by a licensed Electrician that this is acceptable but I seem to keep reading 18" depth is required. The line is served by a 40 Amp breaker. Can you clarify? Thanks
 
  #2  
Old 03-20-20, 06:58 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,895
Received 477 Upvotes on 393 Posts
You confusing your terms. Rigid and PVC are two different types of conduit. Rigid is steel pipes that thread together. There is no rigid PVC.
 
  #3  
Old 03-20-20, 07:01 AM
B
Member
Thread Starter
Join Date: Nov 2001
Location: usa
Posts: 548
Received 2 Upvotes on 2 Posts
Ok thanks for that clarification. So it was buried in PVC not rigid steel.
 
  #4  
Old 03-20-20, 08:30 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,054
Received 3,420 Upvotes on 3,066 Posts
Any PVC conduit needs to be buried 18" deep.
Heavy wall metal conduit doesn't need to be as deep.
 
  #5  
Old 03-20-20, 07:15 PM
B
Member
Thread Starter
Join Date: Nov 2001
Location: usa
Posts: 548
Received 2 Upvotes on 2 Posts
I'm seeing some conflicting information suggesting that GFCI protection lessens the depth to only 12". Can you clarify?
 
  #6  
Old 03-21-20, 06:05 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,756
Received 675 Upvotes on 573 Posts
Yes. If the wires/circuit are GFCI protected before it enters the ground, and is 20 amps or less, and is 120 volts or less, you are only required to bury it 12" deep in most locations. (Table 300.5 2017 NEC)

There is no rigid PVC.
Article 352 Rigid Polyvinyl Chloride Conduit: Type PVC (2017 NEC)

Note: Rigid metal or Intermediate metal conduit is only required to be buried 6" in most locations.
 

Last edited by Tolyn Ironhand; 03-21-20 at 09:36 AM. Reason: added additional info
  #7  
Old 03-21-20, 07:24 AM
B
Member
Thread Starter
Join Date: Nov 2001
Location: usa
Posts: 548
Received 2 Upvotes on 2 Posts
Thanks for clarifying that. So not to sound dense - so if the circuit was 40 Amps and GFCI protected before entering the ground it would need to go 18" down not 12"? Did code years ago require less burial depth? I live in a very old house and I see PVC run above ground...

Why does the Amperage of the circuit affect the burial depth?
 
  #8  
Old 03-21-20, 08:29 AM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,054
Received 3,420 Upvotes on 3,066 Posts
If it was a long time ago it may have been before the code established a burying depth.
A code established burying depth is typically only followed when an inspection is to be made.
Many homeowners running their own lines just bury the conduit/wire to whatever depth is easiest.

20A or less...... reread Tolyns post #6.
 
  #9  
Old 03-21-20, 09:35 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,756
Received 675 Upvotes on 573 Posts
so if the circuit was 40 Amps and GFCI protected before entering the ground it would need to go 18" down not 12"?
Correct. It would need to be buried 18" down. You could use Rigid or Intermediate metal conduit and only put it 6" down regardless of the fuse or breaker rating.

Did code years ago require less burial depth?
Perhaps in the 1930's

Why does the Amperage of the circuit affect the burial depth?
It's all about safety. A 40 amp circuit has a lot more fault current available so if somebody hit it (which often happens) there would be a bigger boom then on a 20 amp circuit. I should have also mentioned that the circuit is also required to be 120 volts or less. I will edit my previous post.
 
  #10  
Old 03-21-20, 12:27 PM
B
Member
Thread Starter
Join Date: Nov 2001
Location: usa
Posts: 548
Received 2 Upvotes on 2 Posts
Thanks guys for all the responses - much appreciated. So I have something of a dilemma. I had an outdoor line run recently by a licensed, very reputable electrical company. They ran a 40 Amp circuit to an outdoor structure about 100 feet away. To say it was a bear is an understatement. I know it is GFCI protected - not sure but think 120 volts but they only buried it 12". Don't really expect to need to do any work in the area that was trenched. Sprinkler system in place from long ago. No gas lines, sewer/drain lines, etc mostly along a tree line. To dig it up and retrench would be a project. Don't really expect any inspections. There are many things about my house that are not code since it was built 100 years ago - in fact there are 120 volt landscape lights probably installed 30ish years ago where the PVC was run above ground in places & where buried is not 18" down for sure.

Any suggestions?
1. Just leave it as is since realistically will probably never be an issue
2. "Cover it" somehow - shrubs/bushes? Stones?
3. Get it retrenched?
 
  #11  
Old 03-21-20, 12:42 PM
PJmax's Avatar
Group Moderator
Join Date: Oct 2012
Location: Jersey
Posts: 62,054
Received 3,420 Upvotes on 3,066 Posts
Why did they say it was a bear ? Was it all rock ?
If it's in now..... leave it.

Mark it well so that you know where it is.
It's technically not to code but it doesn't mean it's unsafe.
 
  #12  
Old 03-21-20, 12:48 PM
B
Member
Thread Starter
Join Date: Nov 2001
Location: usa
Posts: 548
Received 2 Upvotes on 2 Posts
I was there while they did it - old house, stone, plaster & lathe,etc - nothing was straight forward, etc.(Rarely is in my experience) The trenching part per se was not a bear but the rest was..

I will take your advice and just leave it even though it bothers the part of me that wants things done the right way.

Any recommendations for marking it? Thanks again
 
 