Can you bury THW wire in rigid PVC conduit to a depth of only 12" if GFCI protected? I was told by a licensed Electrician that this is acceptable but I seem to keep reading 18" depth is required. The line is served by a 40 Amp breaker. Can you clarify? Thanks
#4
Any PVC conduit needs to be buried 18" deep.
Heavy wall metal conduit doesn't need to be as deep.
Heavy wall metal conduit doesn't need to be as deep.
#5
Member
Thread Starter
I'm seeing some conflicting information suggesting that GFCI protection lessens the depth to only 12". Can you clarify?
#6
Yes. If the wires/circuit are GFCI protected before it enters the ground, and is 20 amps or less, and is 120 volts or less, you are only required to bury it 12" deep in most locations. (Table 300.5 2017 NEC)
Article 352 Rigid Polyvinyl Chloride Conduit: Type PVC (2017 NEC)
Note: Rigid metal or Intermediate metal conduit is only required to be buried 6" in most locations.
There is no rigid PVC.
Note: Rigid metal or Intermediate metal conduit is only required to be buried 6" in most locations.
Last edited by Tolyn Ironhand; 03-21-20 at 09:36 AM. Reason: added additional info
#7
Member
Thread Starter
Thanks for clarifying that. So not to sound dense - so if the circuit was 40 Amps and GFCI protected before entering the ground it would need to go 18" down not 12"? Did code years ago require less burial depth? I live in a very old house and I see PVC run above ground...
Why does the Amperage of the circuit affect the burial depth?
Why does the Amperage of the circuit affect the burial depth?
#8
If it was a long time ago it may have been before the code established a burying depth.
A code established burying depth is typically only followed when an inspection is to be made.
Many homeowners running their own lines just bury the conduit/wire to whatever depth is easiest.
20A or less...... reread Tolyns post #6.
A code established burying depth is typically only followed when an inspection is to be made.
Many homeowners running their own lines just bury the conduit/wire to whatever depth is easiest.
20A or less...... reread Tolyns post #6.
#9
so if the circuit was 40 Amps and GFCI protected before entering the ground it would need to go 18" down not 12"?
Did code years ago require less burial depth?
Why does the Amperage of the circuit affect the burial depth?
#10
Member
Thread Starter
Thanks guys for all the responses - much appreciated. So I have something of a dilemma. I had an outdoor line run recently by a licensed, very reputable electrical company. They ran a 40 Amp circuit to an outdoor structure about 100 feet away. To say it was a bear is an understatement. I know it is GFCI protected - not sure but think 120 volts but they only buried it 12". Don't really expect to need to do any work in the area that was trenched. Sprinkler system in place from long ago. No gas lines, sewer/drain lines, etc mostly along a tree line. To dig it up and retrench would be a project. Don't really expect any inspections. There are many things about my house that are not code since it was built 100 years ago - in fact there are 120 volt landscape lights probably installed 30ish years ago where the PVC was run above ground in places & where buried is not 18" down for sure.
Any suggestions?
1. Just leave it as is since realistically will probably never be an issue
2. "Cover it" somehow - shrubs/bushes? Stones?
3. Get it retrenched?
Any suggestions?
1. Just leave it as is since realistically will probably never be an issue
2. "Cover it" somehow - shrubs/bushes? Stones?
3. Get it retrenched?
#11
Why did they say it was a bear ? Was it all rock ?
If it's in now..... leave it.
Mark it well so that you know where it is.
It's technically not to code but it doesn't mean it's unsafe.
If it's in now..... leave it.
Mark it well so that you know where it is.
It's technically not to code but it doesn't mean it's unsafe.
#12
Member
Thread Starter
I was there while they did it - old house, stone, plaster & lathe,etc - nothing was straight forward, etc.(Rarely is in my experience) The trenching part per se was not a bear but the rest was..
I will take your advice and just leave it even though it bothers the part of me that wants things done the right way.
Any recommendations for marking it? Thanks again
I will take your advice and just leave it even though it bothers the part of me that wants things done the right way.
Any recommendations for marking it? Thanks again