Installed new LED lights in garage and keeps popping circuit off


  #1  
Old 05-23-20, 07:29 PM
J
Member
Thread Starter
Join Date: Apr 2008
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Installed new LED lights in garage and keeps popping circuit off

Bought some super bright LED lights for the garage. They come with sockets to wire into the existing location then I just screw these LEDs into this socket like a light bulb. These sockets only have 2 small metal connectors. (PIC ATTACHED)

The old LED lights that were up there have a copper ground, black and white wire. Not exactly sure what to do with the ground wire. There is one switch for the 5 garage lights.

I took off the old light. Removed the old ground wire from the old led. There were still 2 copper wires connected in the box.

I connected the black wire and white wire to the connectors you see in the picture. The adapter is plastic by the way and not ceramic.

When I turn on the lights the circuit shuts down each time after the LED light comes on for 1/2 second.

Any ideas

 
Attached Images  
  #2  
Old 05-23-20, 08:30 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,895
Received 477 Upvotes on 393 Posts
Make and model of the new LED? Could they be 12 volt instead of 120 volt?
 
  #3  
Old 05-24-20, 03:02 AM
M
Member
Join Date: Sep 2019
Location: Canada
Posts: 1,782
Received 258 Upvotes on 231 Posts
Have you tried it without the LED Bulb installed?
 
  #4  
Old 05-24-20, 04:30 AM
P
Group Moderator
Join Date: Mar 2003
Location: NC, USA
Posts: 25,953
Received 1,764 Upvotes on 1,577 Posts
It sounds like you have a short somewhere. Removing all the light bulbs and turning on the switch will confirm. Since you were not connecting the ground wires it's possible one of them is touching the hot. You might have to take each lamp holder down and confirm how the ground wire is folded underneath.
 
  #5  
Old 05-24-20, 04:33 AM
B
Member
Join Date: Oct 2015
Location: Ct.,USA
Posts: 2,664
Received 235 Upvotes on 208 Posts
If the new sockets each contain a power supply for the DC LED bulb, five sockets in parallel maybe reducing resistance and increasing current above breaker rating. Verify operation with only 1 socket powered. If OK, keep powering one additional socket until problem reoccurs. Will have to run new circuit for the remaining LEDs.
 
  #6  
Old 05-24-20, 07:59 AM
J
Member
Thread Starter
Join Date: Apr 2008
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
I will do that now......Thanks for the reply
 
  #7  
Old 05-24-20, 08:03 AM
J
Member
Thread Starter
Join Date: Apr 2008
Posts: 4
Upvotes: 0
Received 0 Upvotes on 0 Posts
Here is what I purchased: https://www.amazon.com/gp/product/B0...?ie=UTF8&psc=1

There are 5 lights on the circuit in total. I have only installed one new LED at this point. I will verify if the copper is folded weirdly in the box as well.
 
  #8  
Old 05-24-20, 08:54 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,895
Received 477 Upvotes on 393 Posts
Everything looks compatible. I would try it without the LED screwed in. If it still trips, then you have a wiring issue.
If it does not trip then one of the LED might be defective.
 
  #9  
Old 05-24-20, 12:23 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 4,960
Received 158 Upvotes on 144 Posts
Hi, so that pic that device is actually a keyless fixture and should be installed onto a 4” round box, correct? was there a fixture on this before and did it work? post a pic of the box where you intend to install this.
Geo
 
 