Bathroom lights out

Bathroom vanity light and ceiling light on same circuit both went out after years. Breaker is fine and reset and getting power. Changed switch and both fixtures but no lights. Tester beeps on both fixtures when switch is on. I’m stumped...
Any help would be really appreciated!
 
  #2  
Old 06-28-20, 09:34 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,758
Received 676 Upvotes on 573 Posts
A non-contact tester will beep if there is power there but will not tell you if there is an open neutral. You need to use a voltmeter and check if you have 120 volts between hot (black) and neutral (white) at the light. If not then you have to start working backward until you find the loose connection.

Have you changed any switches or receptacles recently?
 
N3V3R D0N3 voted this post useful.
  #3  
Old 06-28-20, 01:52 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 4,960
Received 158 Upvotes on 144 Posts
Hi, you did use known good bulbs.
Geo
 
  #4  
Old 06-28-20, 05:29 PM
K
Member
Thread Starter
Join Date: Jun 2020
Location: United States
Posts: 7
Upvotes: 0
Received 2 Upvotes on 2 Posts
Hi, thanks for the advice. No, I haven’t done anything in that bathroom until the lights went out. Then I changed both light fixtures, the switch and the gfi outlet also, even though not on same circuit.
 
  #5  
Old 06-28-20, 05:41 PM
K
Member
Thread Starter
Join Date: Jun 2020
Location: United States
Posts: 7
Upvotes: 0
Received 2 Upvotes on 2 Posts
Yes, first thing I checked. Thanks
 
  #6  
Old 06-28-20, 06:22 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,758
Received 676 Upvotes on 573 Posts
Are the bathrooms near each other? Was the bathroom without power working before you changed the switch, receptacle, and lights in the other bathroom?
 
  #7  
Old 06-29-20, 03:33 PM
K
Member
Thread Starter
Join Date: Jun 2020
Location: United States
Posts: 7
Upvotes: 0
Received 2 Upvotes on 2 Posts
It is 1 bathroom. No work done at all before lights wouldn’t turn on.
 
  #8  
Old 07-12-20, 03:24 AM
K
Member
Thread Starter
Join Date: Jun 2020
Location: United States
Posts: 7
Upvotes: 0
Received 2 Upvotes on 2 Posts
Fixed the problem!

The neutral wire in an outlet in the adjacent bedroom was not making contact.
the electrician who wired the house had the wiring so tight he had to use the push in connections instead of the nuts.
I pushed all the wires in tight and the bathroom lights worked again!
thanks to all who replied to help me!!!
 
N3V3R D0N3 voted this post useful.
  #9  
Old 07-12-20, 04:44 AM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 5,833
Received 367 Upvotes on 327 Posts
I pushed all the wires in tight and the bathroom lights worked again!
Glad you got it working! Though those push-in connectors are notorious for getting loose over time, and it'll likely loosen up again.

If it were me, I would wire-nut on a 4" pigtail to the white/black wires in this box and connect them to the screw terminals. It's not necessarily something you need to do immediately, but those push-in connectors are definitely unreliable over time.
 
N3V3R D0N3 voted this post useful.
  #10  
Old 07-12-20, 09:02 AM
K
Member
Thread Starter
Join Date: Jun 2020
Location: United States
Posts: 7
Upvotes: 0
Received 2 Upvotes on 2 Posts
Good idea, thanks!

That’s a good idea, thanks!
 
  #11  
Old 07-14-20, 01:15 PM
N3V3R D0N3's Avatar
Member
Join Date: Jan 2019
Location: United States
Posts: 19
Received 0 Upvotes on 0 Posts
Hi ksmi4429,
Your solved problem sounds so similar to an issue we're having - bathroom used to receive power, but now does not. Not on the outlet nor the light switch, nor the fan/heater/light fixture in the ceiling.

Can I ask how you found the loose neutral? did you have to check all the outlets in your walls for the loose wire? how did you know to check the adjacent bedroom? I should probably do that, too. Thanks!
 
  #12  
Old 07-14-20, 01:46 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 4,960
Received 158 Upvotes on 144 Posts
Hi N3V3R, Is it just the bathroom that is effected ? if so remove the devices in the bathroom and see if there are any loose connections , any conductors that are back stabbed into the outlets should be attached to the screw terminals.
Geo
 
N3V3R D0N3 voted this post useful.
  #13  
Old 07-14-20, 02:25 PM
N3V3R D0N3's Avatar
Member
Join Date: Jan 2019
Location: United States
Posts: 19
Received 0 Upvotes on 0 Posts
Geochurchi - yes, it's the bathroom that is solely affected. we have a light fixture over the sinks that I install years ago when we had power and there is an old fan/heater/light fixture in the ceiling. I'll check them both next in my troubleshooting process. Thank you.

I went through most of the adjacent bedroom's outlets and checked for loose white wires. None. They're all the old 'back-stabbed' variety. So you're suggesting that in the bathroom, I should remove those backstabbed wires and re-install them to the screw terminals? I suppose I could do that. Thanks!
 
  #14  
Old 07-14-20, 04:20 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 4,960
Received 158 Upvotes on 144 Posts
Yes, change everything to the screw terminals, if it’s just the bathroom are sure the circuit breaker isn’t the issue, is this an intermittent problem?
Geo
 
N3V3R D0N3 voted this post useful.
  #15  
Old 07-14-20, 06:01 PM
N3V3R D0N3's Avatar
Member
Join Date: Jan 2019
Location: United States
Posts: 19
Received 0 Upvotes on 0 Posts
Geochurchi, yes, the power failures used to be an intermittent occurrence, but at some point, the bathroom completely lost power. I test each circuit breaker with a voltage tester (red on the breaker, black on the neutral bar). They all seemed good to me.
 
  #16  
Old 07-14-20, 06:41 PM
Geochurchi's Avatar
Member
Join Date: Nov 2012
Posts: 4,960
Received 158 Upvotes on 144 Posts
OK, looks like you will need to go to each device, even anything in the general location, does that bathroom have a GFCI receptacle? if so check it first.
Geo
 
 