Low Voltage Transformer Sizing
Received 0 Votes
I have low voltage lighting in our back yard and after adding some new lighting, the lights at the end of my run are not being powered (there's less than 10V at the end).
I'm using a 300W Transformer (Malibu ML300RTW) and 12G line with about 200 feet total. The line starts at the transformer and runs around our yard with lights spaced about 10 feet apart. I'm not able to connect the transformer to the middle of the 200 foot run unfortunately.
I have 10 LED bollards (2W each) and 5 LED spotlights (4W each). I added 4 sets of LED string lights at 9W each and that's when I overloaded the line.
The lights up to about 150 feet have sufficient voltage, but the lights on the last 50 feet are dim and the last 2 lights won't come on.
Can I replace the 300W transformer with a 400W or 450W transformer to fix this?
Unfortunately replacing the transformer with a larger one will not help.
You only have 75 watts of load on the line. You didn't overload anything. Actually.... even though there is a lot of wire..... there shouldn't be that much drop at the end. It sounds to me like you may have a bad splice.
Some transformers have multiple or changeable voltage outputs. Increasing the voltage slightly could help.
The lights towards the end of a long run will always be dimmer. Unfortunately, at 12v, voltage drop quickly becomes an issue over about 150'.
There are a few options:
1) Some people recommend a loop, basically another 12ga wire coming 'back' from the furthest light and connected back to the transformer (observing polarity so you don't have a short). It's sort of a way to parallel the conductors to get more voltage at the far end. (I've never tried this myself, so I can't say for sure how much it helps)
2) Connect to a higher voltage output as Pete mentioned. You can either use the lower 12v output for the lights 50-100' or closer, and the higher voltage for the further away lights. Or connect them all to the higher voltage. Back in the days of incandescent bulbs, that would mean the closer ones would burn brighter and burn out more quickly. I assume with LED lights, since they have voltage regulators on them anyway, the higher voltage won't bother them. (Pete, can you confirm?)