Pot lights suddenly tripping breaker?


  #1  
Old 03-28-21, 09:57 AM
M
Member
Thread Starter
Join Date: Mar 2021
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Pot lights suddenly tripping breaker?

Hi --

I have a series of 5 pot lights, 10-12 years old, in my kitchen, installed (not by me) when the kitchen was redone in 2010. Never had a problem with them, but now all of a sudden they trip the breaker every time I turn them on.

I replaced the halogens with LED bulbs almost 2 years ago and never really had a problem, though they would flicker a bit at low settings on the dimmer.

The pots are on a circuit with 5 other LFs, all single bulb. Shouldn't be anywhere near enough load to trip the breaker, and never has before.

I've done a bit of reading suggesting that it might be a load issue, but why now when it's never been a problem before? Would love any suggestions. Thanks!
 
  #2  
Old 03-28-21, 10:21 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,895
Received 477 Upvotes on 393 Posts
One of the LED driver unit may have failed and is shorting the circuit.
 
  #3  
Old 03-28-21, 11:14 AM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,756
Received 675 Upvotes on 573 Posts
Is the breaker a standard breaker or is it an AFCI or GFCI breaker?
 
  #4  
Old 03-28-21, 12:24 PM
Z
Forum Topic Moderator
Join Date: Sep 2005
Location: USA
Posts: 5,831
Received 366 Upvotes on 326 Posts
It sounds like you're using LED bulbs, so it's easy to unscrew them and see if one is causing a short. Similarly, it could be a surge took out the dimmer switch. I'd put money on one of the LED bulbs going bad.
 
  #5  
Old 03-28-21, 01:30 PM
M
Member
Thread Starter
Join Date: Mar 2021
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Thanks for the replies. I checked the breaker and it is in fact GFCi. It's never been a problem before. What's different now I wonder?

As far as the bulbs, I took them all out and put in halogens -- same problem. The dimmer is an interesting point though. Whether LED or halogen, if the dimmer is at the lowest level the lights seem to be OK. Increase them the tiniest bit and the breaker trips.

Anyway, I appreciate the suggestions. Keep them coming! After trying the bulbs, my next step was to try a new switch to see if the probem is in there. Does that sound like a reasonable course of action?
 
  #6  
Old 03-28-21, 02:03 PM
Tolyn Ironhand's Avatar
Group Moderator
Join Date: Nov 2007
Location: United States
Posts: 13,756
Received 675 Upvotes on 573 Posts
The cause is likely a ground fault somewhere not an overload.

It would be odd that the lights are on a GFCI. Does this circuit also serve an outside receptacle? Some other wet location like a bathroom?
 
  #7  
Old 03-28-21, 02:22 PM
M
Member
Thread Starter
Join Date: Mar 2021
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
Now that you mention it, it does serve the light in the downstairs powder room near the kitchen, which has a GFCI outlet near the sink. Is the GFCI breaker necessary?

Now I guess the question is, how do you find a ground fault? uninstall and reinstall all the pots?
 
  #8  
Old 03-28-21, 03:31 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,895
Received 477 Upvotes on 393 Posts
I would start by removing all the bulbs. Turn on the switch and see what happens.
 
  #9  
Old 03-28-21, 04:23 PM
M
Member
Thread Starter
Join Date: Mar 2021
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
I took all the bulbs out, and flipping the switch didn't do anything -- breaker didn't trip. Only an issue when there are bulbs -- halogen or LED, doesnt' seem to matter.
 
  #10  
Old 03-29-21, 05:00 AM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,895
Received 477 Upvotes on 393 Posts
You need to inspect the wiring at each fixture. I suspect you have a ground & neutral touching that is setting off the GFCI.
 
  #11  
Old 03-29-21, 07:50 PM
M
Member
Thread Starter
Join Date: Mar 2021
Posts: 5
Upvotes: 0
Received 0 Upvotes on 0 Posts
That's a good start, thanks. Could it also be the switch, which is a dimmer? I could try to replace it and see what happens.
 
  #12  
Old 03-29-21, 08:11 PM
J
Member
Join Date: Sep 2002
Location: welland ontario
Posts: 7,895
Received 477 Upvotes on 393 Posts
If you are replacing the switch I would put a normal switch for testing instead of another dimmer.
 
 