Fluorescent shop lights blinking off in cycles of 20-30 seconds
#1
Member
Thread Starter
Fluorescent shop lights blinking off in cycles of 20-30 seconds
Hello!
I have 2 long rows with multiple F96T12 (2 bulb) fixtures each. Each row is on it's own switch. Both rows began blinking off in cycles every 20-30 seconds. All in unison. Basically, it looks like it does if the main power blinks out for a a half second. I'm assuming the two rows are sharing a neutral for this to happen.
One fixture seems to be affected more than the others, and more so on one bulb. I pulled both bulbs and the others kept doing it. If I turn that row (row 1) off at the switch, the other row (row 2) quits blinking and work as they should. If I do the opposite and turn off row 2, row 1 still continues to blink. One bulb in another fixture that has a bad ballast also has a dim surge to it when the others blink. Pulling those 2 bulbs did nothing to help there either. As far as where to start, I'm assuming on row 1, but.....
Does this sound like a ballast somewhere in the chain creating oscillations or a cyclical surge?
Or more like a wiring issue?
Or what?
I have 2 long rows with multiple F96T12 (2 bulb) fixtures each. Each row is on it's own switch. Both rows began blinking off in cycles every 20-30 seconds. All in unison. Basically, it looks like it does if the main power blinks out for a a half second. I'm assuming the two rows are sharing a neutral for this to happen.
One fixture seems to be affected more than the others, and more so on one bulb. I pulled both bulbs and the others kept doing it. If I turn that row (row 1) off at the switch, the other row (row 2) quits blinking and work as they should. If I do the opposite and turn off row 2, row 1 still continues to blink. One bulb in another fixture that has a bad ballast also has a dim surge to it when the others blink. Pulling those 2 bulbs did nothing to help there either. As far as where to start, I'm assuming on row 1, but.....
Does this sound like a ballast somewhere in the chain creating oscillations or a cyclical surge?
Or more like a wiring issue?
Or what?
#2
Even though each row is on separate switches, are they all fed off the same circuit? If you connect a meter to the circuit can you see the voltage vary?
I would suspect either something is up with the circuit breaker or the connection to the panel. Or there could be some other piece of equipment on that phase/leg that is causing a dip in the voltage.
I would suspect either something is up with the circuit breaker or the connection to the panel. Or there could be some other piece of equipment on that phase/leg that is causing a dip in the voltage.
MrPotatoHead
voted this post useful.
#3
Member
Thread Starter
Putting a meter on it is what I was going to do in the morning. I'm assuming they are on the same circuit, yes. I'll have to see what else is on it, as well.
#4
Member
Thread Starter
No variants or voltage dips at the box. There were dips at the fixtures. I removed the power a few fixtures down to the right from the feed and it stopped. I was able to narrow it down to one fixture fairly quick. With only it removed from the chain, the voltage dips and blinking stopped everywhere else. I'll rewire it and a new ballast one of the coming mornings when it's cooler and hopefully it's good to go.
#6
Member
Thread Starter

Yeah. I had been slowly replacing them, after a ballast failed, with direct wire LEDs with single pins that fit into the existing fa8 tombstone before the corona started and shipping became a process for them. I bought a case of ballasts from a local supply during that time. I have 3 left and will go back to that soon.